Now I can stop saying I'm under the impression.
I've confirmed folks, the beast is indeed real
Now I can stop saying I'm under the impression.
That is not what SER means per the UL Guide Information for "Service Entrance Cable (TYLZ)"Just for clarity- there is no SER cable that is 3 wire. SER means 4 wires- 2 hots, neutral and a bare ground. SEU is a 3 wire cable- 2 hots and a bare ground or neutral or both.
- Type SE Style R - Multi-conductor cable containing an unsectioned, uninsulated conductor cabled with the insulated conductors.
- Type SE Style U - Multi-conductor cable containing an uninsulated conductor that is distributed helically over the insulated conductor assembly.
That is not what SER means per the UL Guide Information for "Service Entrance Cable (TYLZ)"
I'll agree that when we say SER we think of 4 wire. But how I discovered that SER doesn't actually mean 4-wire is when I went in to my supply house and asked for SER. They asked if I wanted 3 or 4 wire. I told them I thought it was only 4 wire. They showed me some 3 wire and also their book on it.It doesn't matter what the guide states. For the purpose of this thread ser for a dwelling is 4 wires and seu is 3 wires-- that is what you get when you order it from the supply company
That is just field use of the terms. There is nothing in the product standard that says that. Both products are available in 2,3 and 4 conductor versions.It doesn't matter what the guide states. For the purpose of this thread ser for a dwelling is 4 wires and seu is 3 wires-- that is what you get when you order it from the supply company
That is just field use of the terms. There is nothing in the product standard that says that. Both products are available in 2,3 and 4 conductor versions.
See page 2, near the top:
Thanks for the education.See page 2, near the top:
Is this permissible ? What distinguishes fire disco from service disco ? Is it determined by where neutral/ground bond occurs ?Fire shut down disconnect outside and Service disconnect inside
Nothing other than the label you put on the outside emergency disconnect. If the label just says it is an "emergency disconnect", then that is what it is. It is still permitted to bond that disconnect to the neutral as it is on the line side of the service disconnect.Is this permissible ? What distinguishes fire disco from service disco ? Is it determined by where neutral/ground bond occurs ?
If you had to argue this to a court, what would you use for substantiation that the AHJ is incorrect to call the outside disconnect the service disconnect and requiring the neutral bonding be done there? It seems that just using different wording on a sign should not be the determining factor.Nothing other than the label you put on the outside emergency disconnect. If the label just says it is an "emergency disconnect", then that is what it is. It is still permitted to bond that disconnect to the neutral as it is on the line side of the service disconnect.
Oops - yes. Good catchDoes the outdoor disconnect have to be an OCPD ?
BTW, you had me confused for a moment when you mentioned that it was SER cable. It's actually 3-wire SEU cable (by youir discription) if I'm not mistaken.
Correct - Iβm badJust for clarity- there is no SER cable that is 3 wire. SER means 4 wires- 2 hots, neutral and a bare ground. SEU is a 3 wire cable- 2 hots and a bare ground or neutral or both.
As Don stated the neutral is bonded in the disconnect whether it is the emergency disconnect or the service disconnect.If you had to argue this to a court, what would you use for substantiation that the AHJ is incorrect to call the outside disconnect the service disconnect and requiring the neutral bonding be done there? It seems that just using different wording on a sign should not be the determining factor.
I see I used the wrong words. I am talking about (and I'm pretty sure you know this) the neutral grounding, not neutral bonding, my bad. If the neutral grounding is done in the outside disconnect then the OP has a problem, if it is done in the inside panel then he does not.As Don stated the neutral is bonded in the disconnect whether it is the emergency disconnect or the service disconnect.
Seems like under the 2020 NEC, a label is all that is required. Before the 2020 NEC, you couldn't do it.I will restate that an AHJ is going to probably want more than a label to allow the neutral grounding to be done inside at the panel instead of outside at the disconnect.
Thanks! I guess I'm either going to have to comment less or buy a 2020 code book. BTW, where would one find that in the 2020?Seems like under the 2020 NEC, a label is all that is required. Before the 2020 NEC, you couldn't do it.
Cheers, Wayne
230.85 Emergency Disconnects.
For one- and two-family dwelling units, all service conductors shall terminate in disconnecting means having a short-circuit current rating equal to or greater than the available fault current, installed in a readily accessible outdoor location. If more than one disconnect is provided, they shall be grouped. Each disconnect shall be one of the following:
(1) Service disconnects marked as follows:
EMERGENCY DISCONNECT,
SERVICE DISCONNECT
(2) Meter disconnects installed per 230.82(3) and marked as follows:
EMERGENCY DISCONNECT,
METER DISCONNECT,
NOT SERVICE EQUIPMENT
(3) Other listed disconnect switches or circuit breakers on the supply side of each service disconnect that are suitable for use as service equipment and marked as follows:
EMERGENCY DISCONNECT,
NOT SERVICE EQUIPMENT
Markings shall comply with 110.21(B).
Or open a free account at nfpa.org and read it online at nfpa.org/70. No cut and paste, though.Thanks! I guess I'm either going to have to comment less or buy a 2020 code book.