I was gonna run #3 copper thhn in conduit for a 100amp service. Does stranded vs solid matter?
I was gonna run #3 copper thhn in conduit for a 100amp service. Does stranded vs solid matter?
(C) Stranded Conductors. Where installed in raceways,
conductors 8 AWG and larger, not specifically permitted or
required elsewhere in this Code to be solid, shall be
stranded.
If it is outdoors in a conduit then it must have a "W" in it. Most THHN wire is dual rated as THWN also.Thhn or thwn? Not sure because the drip loop is exposed to the weather
Man up. Wear gloves if you have to.Well 3 solid is a bit tough to get in a conduit.
When you mentioned the #3 solid I wondered where in the world you would find that animal.
And if you did find that animal it is likely to be bare conductor instead of insulated.
I'll bet it will be lot's of fun rolling it off the real..:lol:Actually, the animal (#3 solid) would be a bear to bend/work with...................
You all may now groan at my bad pun.
Stripping it would be a hairy task.I'll bet it will be lot's of fun rolling it off the real..:lol:
Actually, the animal (#3 solid) would be a bear to bend/work with...................
You all may now groan at my bad pun.