service wire

Status
Not open for further replies.
Straight, bends doesn't matter.

(C) Stranded Conductors. Where installed in raceways,
conductors 8 AWG and larger, not specifically permitted or
required elsewhere in this Code to be solid, shall be
stranded.
 
310.3 Stranded Conductors. Where installed in raceways,
conductors of size 8 AWG and larger shall be stranded.

Exception: As permitted or required elsewhere in this
Code.

Rob got it, I type way too slow again.
 
Last edited:
When you mentioned the #3 solid I wondered where in the world you would find that animal. I would be almost as surprised if you found a THHN that did not also have a THWN rating, but, to answer, a "W" conductor is needed both due to the exposure at the weatherhead and being inside an outdoor raceway. (THWN, RHW, XHHW, etc)

(sorry, Dennis... I am slow this mornin')
 