I know they make you use the 60deg column when se cable is ran inside a dwelling. So there is no problem using the 75deg column for a riser outside correct?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
no problem, and if it's a service don't forget the advantage of 310.15(B)(6)
 

jwjrw

Senior Member
Which allows me to use 4/0 al at 200 amps while 310.16 says only 180amps correct? The way Gus worded his post made me think I missed something.
 

Volta

Senior Member
Location
Columbus, Ohio
As in (B)(6) can be used on both the line and load side of the disconnect, as long as those conductors serve 100% percent of the load.
 

iwire

Moderator
Staff member
Location
Massachusetts
As in a back to back installation correct.

Yes and as in a feeder that may run 100s of feet to a subpanel as long as that sub panel supplies the entire load of the dwelling.

You could have a meter / main breaker combo outside and use 310.16(B)(6) to size the feeder that runs from there into the panel.
 

jwjrw

Senior Member
As in (B)(6) can be used on both the line and load side of the disconnect, as long as those conductors serve 100% percent of the load.

Gotcha. I had it right but wanted to make sure. Its going to be cheaper to run SE instead of 2" rigid thru roof.
 