The Final results?
The Final results?
Well, it certainly has been a while since I have posted anything on this topic, but the results are in!
The engineer of record for the project, as well as Eaton (Cutler Hammer) have come up with an explanation and justification of the condition they have created. They say that everything is operating within U.L. test conditions and specifications and that 140F is acceptable as an operating temperature.
We required a letter, sealed and signed by the engineer, stating this. The engineer provided the letter, and it appears that a Certificate of Occupancy will be issued presently.
I am very disappointed that I have not heard back from Underwriter's Laboratory after filing a field report concerning this issue with them. They have not even bothered to tell me that my concerns were not warranted (if indeed this is the case). What good is it to have a third party testing agency that you must rely on for approvals of products if you cannot get them to follow up on a jurisdictional concern? I do not blame the engineer and Cutler Hammer for doing everything they could think of to support their design and products. I DO blame an agency like U.L. for not at least following through on a concern from a jurisdiction.
Good luck to all out there who run into this condition in the future. Let's hope that these devices truly are safe at this operating temperature. I believe they will be safe, but I have concerns about the life expectancy at this constant operating temperature. And let's hope that third party testing agencies take jurisdiction's inquiries seriously and at least respond to the concerns.
Thanks for all of your replies!