yes its required 210.4(b) and its ALL multiwire branch circuits not just lighting as of 2008 code. In the near future I suspect a new requirement of dedicated nuetrals for every circuit but that hasn't happend yet
In the near future I suspect a new requirement of dedicated neutrals for every circuit but that hasn't happend yet
How about almost all?I wouldn't bet on it.![]()
With the mandate for AFCI on new construction residential, shared neutrals should disappear. They are such a troubleshooting issue anyway.
I agree. I find it funny how there is continuing efforts to dumb things down but, the NFPA and OSHA feel it's neccessary to have a definition of Qualified Person.They are fine if installed properly. It's when unqualified fingers get into them and screw things up, when the problems begin.
The subject is MWBCs.Then in effect, are you saying when I look in a commercial panel, every breaker should be a 3 pole breaker ?
But if I'm putting in 3 rows of 120v lighting, you know I'm only pulling 1 neutral. Otherwise the conduit is getting larger. And if someone does a new build, you know they are sharing neutrals. Therefore, your expecting to see all 3 pole breakers. Which means one shorted ballast will make the whole floor dark. You see what I'm getting at.The subject is MWBCs.
Not necessary when separate neutrals are used for wye load circuits. So you can't tell without a deeper look.
If single phase phase-to-phase loads are used, you could have a whole lot of two pole breakers.
Pretty much everyone sees what you are getting at :happyyes: unless they are in the darkBut if I'm putting in 3 rows of 120v lighting, you know I'm only pulling 1 neutral. Otherwise the conduit is getting larger. And if someone does a new build, you know they are sharing neutrals. Therefore, your expecting to see all 3 pole breakers. Which means one shorted ballast will make the whole floor dark. You see what I'm getting at.
If the voltage to ground does not exceed 120 volts, handle ties are acceptable for single phase line to line loads....most of the time a two pole breaker is used, but the code does not require that....
The minimum code requirement is only for handle ties, since the goal is to make sure the neutral is not carrying current when you are going to work on luminaires connected to only one phase. It is perfectly fine to have individual phase or fixture run switches downstream, since the disconnect will still affect all phases. Even the handle ties without common trip will cause maintenance headaches. (But headaches do not justify live work.)Pretty much everyone sees what you are getting at :happyyes: unless they are in the dark.
FWIW, three 1P breakers with handle tie is not the same as a common trip 3P breaker. The handle tie is not an assurance that all breakers will be deenergized when one trips... but there is a definite possibility of that occuring....
...and the only sure way of preventing that is to run individual circuits.
How about that the fuses are not going to be used as disconnects?How can the code require that on circuits over 150 volts to ground if we are allowed to use fuses? I never understood this:roll:
In a situation where actual common trip is required, then fuses do seem inappropriate.
In Don's post it seen he indicated that common trip was required for single phase MWBC's where the voltage is above 150 volts to ground?, I know there are some codes that do require common trip like autotransformer's, in 450.5(B)(2)(a)
And 647.4 are two locations that I know of, and the latter even allows fuses which doesn't make sense to me.
But I don't know anywhere the code requires a common trip just because the voltage to ground is higher then 150 volts??