Sharing neutral

Status
Not open for further replies.
And the calculated neutral currents would be 4.7, 6.6, 7.4 and 8.1 respectively. It is interesting for the circuit 14, 16 combination that the calculated current is greater than the measured current. I wonder why.

I'm more curious as to why my calculated neutral load is 3.48 instead of the 4.7 that you got. The rest are close enough 6.56, 7.46 and 8.11
 
I'm more curious as to why my calculated neutral load is 3.48 instead of the 4.7 that you got. The rest are close enough 6.56, 7.46 and 8.11
Tom,
Probably because I put the wrong numbers in my spreadsheet. I ran it again and got the 3.48 like you did.
 
Status
Not open for further replies.
Top