I've never seen a luminaire that has a yoke. I stand by my original statement in that a multipole (or handle tied) breaker is not required.
ryan_618 said:I've never seen a luminaire that has a yoke.
I guess you could say 310.15(B)(4)(a) requires this but if they meant (a) to cover non-linear loads what would be the need for (c)?
Anyone with the 2002 NEC Handbook should take a look at the commentary following 310.15(B)(4). They present a lot of info on Non-Linear loads and the effect on equipment.
Here are a couple of quotes.
The data were obtained from consultants, equipment manufacturers, and testing laboratories, and included hundreds of feeder and branch circuits involving 3-phase, 4-wire, wye-connected systems with nonlinear loads. The data revealed that many circuits had neutral conductor current greater than the phase conductor current, and approximately 5 percent of all circuits reported had neutral conductor current exceeding 125 percent of the highest phase conductor current.
125% sounds extremely damaging until they go on to point out.
quote:.....the total continuous load on any overcurrent device located in a panelboard should not exceed 80 percent of its rating (the exception being assemblies listed for continuous operation at 100 percent of its rating). Because the neutral conductor is usually not connected to an overcurrent device, derating for continuous operation is not necessary. Therefore, neutral conductor ampacity is usually 125 percent of the maximum continuous current allowed by the overcurrent device.
There is much more in the handbook it is worth a look.
http://www.mikeholt.com/cgi-bin/codeforum/ultimatebb.cgi?ubb=print_topic;f=11;t=003000
Why?wavector said:Most electricians, including myself, I have worked with do not like sharing neutrals.
It is around here. Why aren't they in Alabama?While this is code for multiwire branch ciruits, it is not enforced.
Remember, in the event of a shock or fire, you are responsible for adhering to the NEC, even if the local jurisdiction is lax in their enforcement. Someday, in the event of an incident, the insurance company could be the AHJ...But for the most part...
wavector said:Let me restate some of this. If a multiwire branch circuit is used to feeder a nonlinear load, such as flourescent lighting electronic or magnetic ballast, the neutral that is shared must derated.
wavector said:Most electricians, including myself, I have worked with do not like sharing neutrals.
wavector said:If there is a nonlinear load, the neutral must be derated.
iwire said:wavector said:Let me restate some of this. If a multiwire branch circuit is used to feeder a nonlinear load, such as flourescent lighting electronic or magnetic ballast, the neutral that is shared must derated.
Really? :?
Can you cite a code section that requires this?
wavector said:Most electricians, including myself, I have worked with do not like sharing neutrals.
Don't speak for others as my friends and I run as many MWBCs as possible. 8)
Doing so saves material and reduces voltage drop issues.
wavector said:If there is a nonlinear load, the neutral must be derated.
Again....a code section that backs that up?
90.5(C) Explanatory Material. Explanatory material, such as references to other standards, references to related sections of this Code, or information related to a Code rule, is included in this Code in the form of fine print notes (FPNs). Fine print notes are informational only and are not enforceable as requirements of this Code.
wavector wrote:
Most electricians, including myself, I have worked with do not like sharing neutrals.
Don't speak for others as my friends and I run as many MWBCs as possible.
Doing so saves material and reduces voltage drop issues.
I personally disagree with this proposal, and plan on commenting in that CMP-2 should reconsider their decision. But if you feel the technique is dangerous, you should write in to support them.2-10 Log #2679 NEC-P02 Action: Accept in Principle
(210.4)
Submitter: Dorothy Kellogg, American Chemistry Council
Panel Meeting Action: Accept in Principle
Revise the last sentence of 210.4(A) in the present code to read: "All conductors of a multiwire branch circuit shall originate from the same panelboard or similar distribution equipment."
Revise 210.4(B) in the present code to read: "Disconnecting Means. Each multiwire branch circuit shall be provided with a means that will simultaneously disconnect all ungrounded conductors at the point where the branch circuit originates."
Panel Statement: The panel has accepted the submitter's recommendation, but has revised the text in 210.4(A) and (B) to accomplish the intent of the submitter.
busman said:Bob,
Do you have a reference for the "1.73 times the phase current" being the worst case? I would have said that if ALL the current were at the 3rd harmonic of the voltage frequency, then the neutral current is 3 times the phast current.
The more I thought about this, I might be thinking wye and you thinking delta. Never mind.
Mark
Bob, try searching the page for the text "twice" with your browser's "FInd" text feature. You will see Mike Holts statement, "Nonlinear loads cause the neutral to carry as much as twice the phase current."iwire said:What is your point Roger?