ramsy
NoFixNoPay Electric
- LA basin, CA
- Service Electrician 2020 NEC
Mike Holt's publications offer several unqualified opinions that choose to error on the side of caution. In his 1999 NEC study guide Mr Holt advises, "3? 4-wire wye's that supply nonlinear loads ..can produce unwanted and potentially hazardous harmonic (neutral) current(s) ..as much as twice the phase conductor current. The neutral conductor must be sized to carry the excessive harmonic neutral current to prevent the conductor from overheating and possibly causing a fire or equipment damage, Fig. 5-3."
Would you agree that my assesment of Mr. Holts opinion fairly reads his choice to error on the side of caution?
Now check me here, but I believe Delta connected loads, (ie) motors, and some devices may also dampen their own harmonics on wye systems.
I would like to assume a Wye line to delta load dampens harmonics just like a delta xfmr, but without testing this myself or finding evidence elsewhere, I will phrase it as a question for anyone who might hazard a more informed opinion. Scott35 ?
Would you agree, if your practical experience finds no evidence for this kind of harmonics, that should not dictate the limits of what others will encounter in the field? Especially for troubleshooters, who are called in specifically for wireing problems?iwire said:The fact is neutrals are not overheating on a regular basis on non-linear loads...No mater if you use two wire or MWBCs the harmonic issue (if there is one) will still be an issue for the panel, feeder and transformer.