DBoone
Senior Member
- Location
- Mississippi
- Occupation
- General Contractor
Get rid of junction box, use disco.
Bonding jumpers are sized per size of entrance conductor, 250.102. You are gonna more than just interior wall. Frames, beams, chassis,etc.
NM and plastic boxes are fine.
He, not being an electrician, is why these units get miswired and people get killed.
100A 120/240V?
I haven't looked closely yet but assumed the walls, beams, etc were all connected so Bonding to the wall would bond the entire enclosure.
120/240 and was thinking either a 60A or 100A panel
Mini-Split is 208/230V , MOCP 15, MCA 7.95 so will use 14-2 on double pole 15A breaker
I will look at 250.102 to size Bonding jumper
How would you set up your disco and panel. What size and what wiring method