DBoone
Senior Member
- Location
- Mississippi
- Occupation
- General Contractor
If you (or someone) is feeding a 125A panel with more than a 125A feeder than that is a violation to begin with. You can't feed another panel with more than the rating of the panel. You can feed the same or less but not more.
Yes that's right. I don't like not knowing how power will be provided on these big jobsites.
So my original idea was just land incoming power on the Main Lugs outside. Feed the inside panel from a 60 amp breaker. That leaves 2 spaces still available outside for future add on.
As as far as the separate structure having a main disconnect in one motion of the hand someone could turn off every breaker (4 spaces)
After reading the reply from Ben it sounds like he suggests I need to install a breaker with a hold down kit outside. Label it Main and then anybody that has a clue will know to back feed it with the incoming power. Then install another breaker to feed inside.
If I need the back-fed Main then sounds like a better design for me would be to exchange my 4/8 loadcenter for an 8/16 and use a 100 or 125 amp breaker for my Main. Then I can feed inside with my 60 and still have some space for future additions such as a service receptacle on the exterior.