goldstar said:I agree with the others on this. You need to locate and correct the problem not hide or mask it. Make sure you have a helper with you. Connect something to the source of the power (like a meter or a keyless fixture with a light bulb). Then either you or the helper go down and switch off breakers one at a time until the voltage disappears. If it doesn't disappear throw the main breaker (but I'd be willing to bet it's one of the branch circuits). If it disappears when you throw the main that will lead us down another path of possibilities. I would start by leaving the main off and then shutting off all the branch circuit breakers and then turn on the main. If the voltage hasn't returned then switch on each breaker, one at a time, until the voltage re-appears. Once it appears, switch that breaker off but keep going to make sure there isn't more than one breaker causing the problem. At least that way you can determine which brancdh circuit(s) is causing the problem.
You also mentioned that you upgraded the service from 60 amps to 100 amps. Was there any chance that any of the original circuits are or were K & T ? If so, chances are that either a hot or a neutral came in contact with an ungrounded portion of the piping system. If there is RX cable inside the house there could be a sheetrock screw shot through the sheething of the NMC. Let us know how you make out.[/Q
I agree that is good way to determine if there is a problem being caused by a branch circuit. But if there is a ground fault and the water system is bonded
why would it not trip the breaker? I am not trying to play the expert I just have a feeling that there is a open neutral problem. As all
of use that have been in the trade for a long time know there are still surprises and we are still learning. Well I am. Please let us know the results.