PVC conduit, infinite source:
3 AWG- X= 0.047 R=0.25 per 1000 feet
8 AWG- X=0.052 R=0.78 per 1000 feet
X= 0.01175 R=0.0625
X=0.013 R=0.195
Total X=0.02475
Total R=0.2575
View attachment 2555236
0.0006125625 + 0.06630625 = 0.0669188125
0.0669188125 square root= 0.2586867072348326 ohms
463 amps at 120 volts.
A 100 amp breaker it will take about 10 seconds on average to open, 15 tops.
An 80 amp breaker will take 5 seconds on average to open, 8 tops.
5 seconds is legal for table 41.1, and I'd argue up 10 seconds could work with our systems.
15 seconds is just getting dangerous and not recognized anywhere.