the NEC does not say that though. I don't see how you could enforce such a thing.
90.1 (C) points us in that direction.
the NEC does not say that though. I don't see how you could enforce such a thing.
It does nothing if the sort.90.1 (C) points us in that direction.
Most modern 120v appliances are available with 2-prong plugs, when only plastic parts are in contact with users.If double insulated.
Yes, and you exercised your right to exceed the NEC's 250.140 minimum standard, by removing touch potential with 3-wire European laundry appliances using 240v light bulbs & controls, which never put frame in same path of current carrying conductors.This would give insight that an effective ground fault current path is the primary means by which protection against electrocution is achieved and not ground fault circuit interrupters which are essentially a back-up.
It does nothing if the sort.
Most modern 120v appliances are available with 2-prong plugs, when only plastic parts are in contact with users.
The persistent 3-prongs remain refrigerators, microwaves, laundry machines, room air conditioners, range/ovens, and their hood light/vents
Yes, and you exercised your right to exceed the NEC's 250.140 minimum standard, by removing touch potential with 3-wire European laundry appliances using 240v light bulbs & controls, which never put frame in same path of current carrying conductors.
Roger that. Inspectors can red tag 3-prong appliance cords plugged into such GFCI protected outlets missing EGC wiring.
However, there is always exceptions in the National Exceptions Code (NEC).
250.114 Exception: Listed tools, listed appliances, and listed equipment covered in 250.114(2) through (4) shall not be required to be connected to an equipment grounding conductor where protected by a system of double insulation or its equivalent. Double insulated equipment shall be distinctively marked.
That leaves 1 place 3-prong is mandated:
(1) In hazardous (classified) locations (see Articles 500 through 517)]
And we generally don't think about it until we run into a troubleshooting situation and happen to witness long trip times first hand on such installs.I’ve thought of this issue in the past when sizing pivot laterals. Basically we size for VD to the pivot point, 1400’. Not any thought/planning goes into how long it takes for a fault to open fuses.
And we generally don't think about it until we run into a troubleshooting situation and happen to witness long trip times first hand on such installs.
My guess is this is part of reason why newer pivot equipment for some time now has had Class CC fuseholders installed in it where old equipment had class R fuseholders.
By class R I'm talking about are the typical RK5 fuses you would see used for general purpose time delay applications.Can you explain the difference between class CC fuses and R fuses?
Cc fuses are 600 v current limiting and only go up to 30 amps. Yes I know there's at least one manufacturer that makes a 35 amp version.Can you explain the difference between class CC fuses and R fuses?
Cc fuses are 600 v current limiting and only go up to 30 amps. Yes I know there's at least one manufacturer that makes a 35 amp version.
They are small and don't take up a lot of panel space.
It is only made in 1/10 to 30 amp ratings, but has different trip curve than a RK5 fuse of same amp rating. Also has different trip curve than other general purpose miniature fuses that are same physical sizeSmaller fuse blow faster. I guess that makes sense.
Electrical safety statistics - Nickle Electrical
About 400 deaths and 4,000 injuries are reported each year due to electrical hazards. Here are a few statistics about electrical safety.www.nickleelectrical.com
GFCIs have helped immensely when 250.4 (5) has fallen short.
View attachment 2555231
They certainly Do. Not always but generally, yes.GFCIs don’t prevent shocks. They respond after it starts.
GFCIs don’t prevent shocks. They respond after it starts.
They don't prevent all shocks. One example where they possibly do is with wet location conditions sometimes there is fault conditions that make them trip before a user is subject to possible shock. But if the user is suddenly introduced as the fault path he will be shocked and the GFCI will trip after it starts, presuming enough current flows to initiate trip. ~ 5ma still wakes a person up when it passes through them.GFCIs don’t prevent shocks. They respond after it starts.