(B) Feeders.
For a feeder rated 100 amperes through 400 amperes, the feeder conductors supplying the entire load associated with a one-family dwelling, or the feeder conductors supplying the entire load associated with an individual dwelling unit in a two-family or multifamily dwelling, shall be permitted to have an ampacity not less than 83 percent of the feeder rating.
If no adjustment or correction factors are required, Table 310.12(A) shall be permitted to be applied for conductors or cables rated 75°C (167°F) or greater.