Sure, but there are other common outdoor wiring methods limited to the 60C ampacity, such as UF, LFMC, and LFNC.If it is, that negates the use of NM, period.
Cheers, Wayne
Sure, but there are other common outdoor wiring methods limited to the 60C ampacity, such as UF, LFMC, and LFNC.If it is, that negates the use of NM, period.
The reference in 334.80 to 310.14 is not an open ended allowance that points all the way back to 310.12. There is a limiting factor of a reference to the "Tables in 310.15"I see that took me for a loop the current wording in 334.80 references -> 310.14 then 310.14 references -> 310.15 which references 310.12
The 2026 wording just says you cant use the table, you can still use the 83%
2026 310.12(B):
At the end of the day, this setup appears to be on the exterior of the building, which I asked about but the OP has neither confirmed nor denied.
If it is, that negates the use of NM, period.
The 2/0 Cu SER cable or 4/0 Al SER would be permitted ampacity wise.The main service disconnect is on the exterior on the exterior of the building.
The panelboards are inside the building.
All that is on Post #1