Augie,
In the IFC 2006 904.11.2 System interconnection.-"The actuation of the fire extinguishing system shall automatically shut down the fuel or electric power to the cooking equipment. The fuel and electric supply reset shall be manual." Also articles 904.5 Wet-chemical systems and 904.11 Commercial cooking systems direct you back to NFPA 17A. These would not require anything beyond previous stated NFPA 17A requirements.
Rick,
Interpretation of this is one of those things that is almost humorous. I talked with various enforcement folks in the past few days and most state "everything" under the hood must be disconnected. When pressed for details they quote NFPA of Fire Codes stating what you quoted. The "devil is in the details", one Fire Marshal stating that anything electrical is a potential "heat source". It appears to be one of those areas where overlapping jurisdiction and misinformation has taken precedence over Code.