pierre
Senior Member
- Location
- Westchester County, New York
Re: side stepping arc fault breakers
406.2 Receptacle Rating and Type.
(B) Receptacles and cord connectors shall be rated not less than 15 amperes, 125 volts, or 15 amperes, 250 volts, and shall be of a type not suitable for use as lampholders.
210.3 Rating.
...The rating for other than individual branch circuits shall be 15, 20, 30, 40, and 50 amperes.
When installing more than one receptacle (a single receptacle is 1 receptacle, a duplex receptacle is 2), it is other than an "individual branch circuit", so one would have to install a 15 or 20 ampere branch circuit to an average bedroom [210.52(A)(1)&(2)] as they generally have more than 1 receptacle.
210.12(B)would come into play and Arc-Fault protection would be required.
Pierre
I had to read some of the last posts to see what was generating so much interest - I only read the last ten or so. I could be way off the mark here, but posted anyway
406.2 Receptacle Rating and Type.
(B) Receptacles and cord connectors shall be rated not less than 15 amperes, 125 volts, or 15 amperes, 250 volts, and shall be of a type not suitable for use as lampholders.
210.3 Rating.
...The rating for other than individual branch circuits shall be 15, 20, 30, 40, and 50 amperes.
When installing more than one receptacle (a single receptacle is 1 receptacle, a duplex receptacle is 2), it is other than an "individual branch circuit", so one would have to install a 15 or 20 ampere branch circuit to an average bedroom [210.52(A)(1)&(2)] as they generally have more than 1 receptacle.
210.12(B)would come into play and Arc-Fault protection would be required.
Pierre
I had to read some of the last posts to see what was generating so much interest - I only read the last ten or so. I could be way off the mark here, but posted anyway