Marty Lustig
- Prairie Village, KS
Does Siemens make a 15 amp plug-in TWO pole AFCI/GFCI circuit breaker? If you know of a source, I'd appreciate a link.
Jaggedben, thank you. When I do Google [h=1]Siemens Q215AFC, what I get is "15-Amp 2 Pole 120-Volt Combination Type Arc Fault Circuit Interrupter by Siemens". But that's not "dual function" AFCI and GFCI. Any other thoughts? Maybe i'm missing something??[/h]Q215AFC
Google it.
Sorry about the bold!! Nothing intended by it.
Jaggedben, thank you. When I do Google Siemens Q215AFC, what I get is "15-Amp 2 Pole 120-Volt Combination Type Arc Fault Circuit Interrupter by Siemens". But that's not "dual function" AFCI and GFCI. Any other thoughts? Maybe i'm missing something??
Thank you, as well, for the Murray lead. But it is also only AFCI, not dual function AFCI/GFCI.Murray MP215AFC is physically the same and also listed for some Siemens panels.
What does combination mean? Series and parallel arcing?15-Amp 2 Pole 120-Volt Combination Type Arc Fault Circuit Interrupter by Siemens. But that's not "dual function" AFCI and GFCI.
GFCI function will not work on handle tied units, current that leaves one pole must return on the load neutral of same pole or it will trip, to get multiwire GFCI you must have a unit with all monitored load wires run through a common sense coil. This applies to all makes/brands of GFCI's.Sorry I missed the GFCI part. No wonder that was too easy. :slaphead:
I'm guessing nobody makes what you're after then. (it would presumably be a Q215DF). If you just need it for MWBCs there may be a handle-tie solution.