Siemens New Tandem AFCI Breakers

Status
Not open for further replies.

mbrooke

Batteries Included
Location
United States
Occupation
Technician
I see your reading material may be an adopted code proposal, a mention of 30mA GFPE removed from CAFCI, and subsequent failure to extinguish an arc, and some feature not part of UL 1699.

The author claims removing 30mA GFPE removes certain arc detection, without disclosing model & date of AFCI used in 2012. I remember similar DIY YouTube demonstrations, but nothing published by an NRTL. However, for sake of argument lets say AFCI's can't extinguish arcs after removing ground fault or hot-neutral imbalance detection.

The damage with existing equipment is more from smoldering than arcing, and not detectable by a GFCI or thermal-magnetic breaker, but it does fail inspection per 110.12(B), and its correction resolves AFCI issues.

AFCI's have forced me to improve my field skills: led me to burn-damage at outlets, burnt bus stabs, crushed cords under furniture, and forced me to engage occupants; to demonstrate reset button, and unplug all appliances before calling me back under warranty.


IMO, I think even more telling is that cords can produce parallel arcing current under 75 amps, and series arcing under 5 amps.

There seems to be a need to decrease sensitivity and curtail full spectrum coverage.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
I see your reading material may be an adopted code proposal, a mention of 30mA GFPE removed from CAFCI, and subsequent failure to extinguish an arc, and some feature not part of UL 1699.

The author claims removing 30mA GFPE removes certain arc detection, without disclosing model & date of AFCI used in 2012. I remember similar DIY YouTube demonstrations, but nothing published by an NRTL. However, for sake of argument lets say AFCI's can't extinguish arcs after removing ground fault or hot-neutral imbalance detection.

The damage with existing wiring & devices in older buildings is more from smoldering than arcing, and not detectable by a GFCI or thermal-magnetic breaker, but it does fail inspection per 110.12(B), and its correction resolves AFCI issues.

AFCI's have forced me to improve my field skills: led me to burn-damage at outlets, burnt bus stabs, crushed cords under furniture, and forced me to engage occupants; to demonstrate reset button, and unplug all appliances before calling me back under warranty.
And not detectable by AFCIs in most cases. Where the wiring method has an EGC, a GFCI or an AFCI with GFP has a better chance of detecting the issue and clearing the circuit before there is a fire. The heat from the poor connection will often result in a ground fault before there is any type of detectable arc, and there can easily be enough heating. even if it is an series arcing fault, to start a fire even with currents below 5 amps. The AFCI does not look for series arcing faults unless the current is 5 amps or more and does not look for a parallel arcing fault unless the current is 75 amps or more.

It remains my opinion that AFCIs without a GFP function are pretty much worthless. However, AFCIs without GFP pass the UL requirements for AFCIs. The standard has never required the GFP function, but that was the only way they could get the device to pass all of UL requirements when they first came out. Over time, the manufacturers found ways to pass all of the tests without the GFP and some have removed those GFP components from their AFCIs as a method to increase the profit margin.
 

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
..Where the wiring method has an EGC, a GFCI or an AFCI with GFP has a better chance of detecting the issue and clearing the circuit before there is a fire...
GFCI's don't see propagating wave forms from all directions.

Searching and identify a Plug-on breaker burning up a bus stab has resolved Leviton's AGTR1 outlet from tripping, installed per 406.4(D)3&4, 50ft away in the kitchen.

Its not the GFCI function that detected up stream events in the fuse box --with only the refrigerator running-- so critical maintenance can avoid further destruction.
 

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
It remains my opinion that AFCIs without a GFP function are pretty much worthless.
GFCI's without AFCI function can also be argued as worthless: See Photo of new GFCI vs Defective Gadget

GFCI Bomb.jpg
GFCI Test & Reset button function normally after this event, which was completely undetected by the GFCI

GFCI Bomb-2.jpg
..The heat from the poor connection will often result in a ground fault before there is any type of detectable arc, and there can easily be enough heating.
Neither heat or anything else tripped this bath GFCI in above photo, which smoked & burned between Hot-Neutral.
The AFCI does not look for series arcing faults unless the current is 5 amps or more and does not look for a parallel arcing fault unless the current is 75 amps or more.
How AFCI's extinguish arcs is debatable, but they are observed in the field extinguishing smoldering and other non-arcing events.

AFCI breakers are known to trip together on same event, and when wiring lights are known to trip with Green & White wires held in opposite hands --at Zero amps-- with switch leg turned off.

AFCI are not superior to GFCI's, but do extinguish events GFCI's can not, since not limited to downstream-current imbalance.

To claim AFCI triggers are limited to arcs is Fake News.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
GFCI's without AFCI function can also be argued as worthless: See Photo of new GFCI vs Defective Gadget

View attachment 2557784
GFCI Test & Reset button function normally after this event, which was completely undetected by the GFCI

View attachment 2557785

Neither heat or anything else tripped this bath GFCI in above photo, which smoked & burned between Hot-Neutral.

How AFCI's extinguish arcs is debatable, but they are observed in the field extinguishing smoldering and other non-arcing events.

AFCI breakers are known to trip together on same event, and when wiring lights are known to trip with Green & White wires held in opposite hands --at Zero amps-- with switch leg turned off.

AFCI are not superior to GFCI's, but do extinguish events GFCI's can not, since not limited to downstream-current imbalance.

To claim AFCI triggers are limited to arcs is Fake News.
The AFCI may or may not detect and clear that circuit. No device on the market can directly detect an clear a joule heating fault...by far the most common fault and likely the type of fault shown in those pictures.
 

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
The AFCI may or may not detect and clear that circuit. No device on the market can directly detect an clear a joule heating fault...by far the most common fault and likely the type of fault shown in those pictures.
AFCI replacements regularly extinguish circuits until burnt remains of old damage is repaired.

Anyone experienced with this knows existing devices replaced with AFCI's can regularly trip until some upstream or downstream burn damage is repaired.

As described in post #46, and similar photos posted on this forum, searching to identify burnt up wiring, bus stabs, or charcoal devices has resolved AFCI issues. Call it joule heating or whatever you want.

To claim AFCI's can't detect this crap is Fake News.
 
Last edited:

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
Its more plausible to me that carbon deposits can create a high resistance path between ground (White) and EGC (Green), similar to holding the 2 wires in each hand, as described in post #49, also known to trip AFCI's.
 

retirede

Senior Member
Location
Illinois
GFCI's without AFCI function can also be argued as worthless: See Photo of new GFCI vs Defective Gadget

View attachment 2557784
GFCI Test & Reset button function normally after this event, which was completely undetected by the GFCI

View attachment 2557785

Neither heat or anything else tripped this bath GFCI in above photo, which smoked & burned between Hot-Neutral.

How AFCI's extinguish arcs is debatable, but they are observed in the field extinguishing smoldering and other non-arcing events.

AFCI breakers are known to trip together on same event, and when wiring lights are known to trip with Green & White wires held in opposite hands --at Zero amps-- with switch leg turned off.

AFCI are not superior to GFCI's, but do extinguish events GFCI's can not, since not limited to downstream-current imbalance.

To claim AFCI triggers are limited to arcs is Fake News.

The purpose of a GFCI is prevent people from being electrocuted by coming into contact with an ungrounded conductor and ground. They are not intended to detect a failure such as that in your photo.

The only way to statistically prove that AFCIs prevent electrical fires would be if the rate of electrical fires started to decrease as AFCIs were implemented. It’s been a while since I’ve looked at the numbers, but there is no downward trend.
 

paulengr

Senior Member
GFCI's without AFCI function can also be argued as worthless: See Photo of new GFCI vs Defective Gadget

View attachment 2557784
GFCI Test & Reset button function normally after this event, which was completely undetected by the GFCI

View attachment 2557785

Neither heat or anything else tripped this bath GFCI in above photo, which smoked & burned between Hot-Neutral.

How AFCI's extinguish arcs is debatable, but they are observed in the field extinguishing smoldering and other non-arcing events.

AFCI breakers are known to trip together on same event, and when wiring lights are known to trip with Green & White wires held in opposite hands --at Zero amps-- with switch leg turned off.

AFCI are not superior to GFCI's, but do extinguish events GFCI's can not, since not limited to downstream-current imbalance.

To claim AFCI triggers are limited to arcs is Fake News.

To claim an AFCI trips on anything other than “arcing” is simply not true. During an arc you get a pulsed square-wave looking waveform. This highly nonlinear waveform is what the AFCI is looking for and what it trips on.

A combination AFCI is as it implies a combined GFCI and AFCI. And in this case I’d agree…it trips in arcing faults and ground faults. Perhaps you were confused or your statements were confusing due to your arrogance?

The inherent problem with this, is with SCR based rectifiers (active front ends) in electronics such as lamp dimmers and switching power supplies they switch on part way through the sine wave which gives it an arc-like waveform. This also causes AFCI trips but they are nuisance trips. Thus the incredibly bad reputation with AFCIs. The AFCI manufacturers have tried to discriminate but the fact is that it’s a balancing act between pinching pennies, false negatives, and false positives. The devices are highly tuned to ULs simulator but real world testing is not so good…see examples below.

Your pictures show a device that most likely underwent one of two failures. The first is overcurrent. There are many cases and reasons why overcurrent would be missed. For instance a 15 A breaker does not trip instantly at 15.000001 A. In fact it can trip at 75-300 A or higher in one cycle but under that current we are dealing with inverse time…the higher the current the faster it trips. A GFCI only device won’t care…current on hot and neutral is identical so no reason to trip. This example most likely shows a breaker failure or a utility fault. Overcurrent device only trips if current is pretty high.

It could also be damage due to a transient (voltage pulse) or even an arcing fault but it is well documented that line to line arcs are rare. Phase to neutral is the most common. An AFCI is programmed to trip on certain waveforms set by UL but not every arc looks like the UL test labs. In fact UL, NEC, and manufacturers have been soundly criticized for mandating AFCIs without any simple scientific explanation behind them.

Plus there are three kinds of arcing faults. In one type the arc is from phase to ground. Your claim that GFCI does nothing is utter nonsense because this is precisely the condition that GFCI is intended to detect and trip on. The second type is phase to neutral or phase to phase. Currents are balanced so GFCI should not trip while almost every AFCI can and does trip. But these are comparatively rare. A fourth type and likely what your device experienced are “series” arcs which is just a loose or open connection. Newer combination AFCIs are supposed to detect and trip on these but the only evidence is in the current signature which is notoriously hard to detect and subject to both false positives and negatives. Nobody will say that AFCIs work every time and nuisance tripping is a problem. But what happens in basic “redneck” YouTube style testing?

Here is a video with a combination AFCI:


A more fancy version, same result:


Ok but surely we can just look at house fires, right?
Yes there is lots of data showing a downward trend but there’s a huge problem with it. The downward trend correlates well with the introduction of GFCIs but the introduction of AFCIs which happened later does not show a change in slope. Thus the data touted by the AFCI manufacturers clearly demonstrates that GFCI protection alone is responsible for the improvements at best and that at worst some other external event is primarily responsible. This is one of the problems with looking at historical trends…correlation does not prove causation. However we can also look at different jurisdictions and compare the results (AFCI vs no AFCI) such as Virginia and North Carolina or Michigan and Indiana. These states have similar demographics. AFCIs were removed from Code in one but not the other. The result? Fire statistics are identical in both cases. This is a far stronger case for correlation than time based data but again no evidence that AFCIs do anything at all.

Here is what Michigan thinks of AFCIs:


The big claim for AFCIs is something called wood pyrolysis. The theory is that a staple driven through an NM to the point where it contacts the hot conductor will slowly char the wood via ground fault currents until it eventually arcs and starts a fire. I know this sounds like a joke but this is actually the mechanism claimed by the CPSC and used as justification for AFCIs. Obviously with wood which is a pretty good insulator there is not nearly enough energy for pyrolysis much less spark ignition but that’s actually the preposterous justification for AFCIs.

There’s more out there, a LOT more.

To accuse others of fake news claims when you don’t have a leg to stand on is right up there with most of the things Bob Acosta has to say. With the same level of arrogance and condescension.

Care to try again with actual scientific evidence?
 

paulengr

Senior Member
The purpose of a GFCI is prevent people from being electrocuted by coming into contact with an ungrounded conductor and ground. They are not intended to detect a failure such as that in your photo.

The only way to statistically prove that AFCIs prevent electrical fires would be if the rate of electrical fires started to decrease as AFCIs were implemented. It’s been a while since I’ve looked at the numbers, but there is no downward trend.

Not true.

A GFCI trips when it detects a ground fault. This is tripping when a shock is in progress. It doesn’t attempt to prevent one in any way.

There is another way to prove AFCIs work not subject to contamination by other events. Take similar jurisdictions where one requires AFCIs and the other does not. If the fire stats are different there is your evidence. They are the same for NC and VA as well as IN and MI on a per capita basis.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The purpose of a GFCI is prevent people from being electrocuted by coming into contact with an ungrounded conductor and ground. They are not intended to detect a failure such as that in your photo.

The only way to statistically prove that AFCIs prevent electrical fires would be if the rate of electrical fires started to decrease as AFCIs were implemented. It’s been a while since I’ve looked at the numbers, but there is no downward trend.
And given the small numbers of new houses compared to existing houses and the fact that the fire stats used to get AFCIs into the code showed that 85% of the dwelling unit electrical fires occurred in dwelling units at least 20 years old, it will be many decades before the effectiveness of AFCIs can be proved or disproved using fire data.
 

retirede

Senior Member
Location
Illinois
Not true.

A GFCI trips when it detects a ground fault. This is tripping when a shock is in progress. It doesn’t attempt to prevent one in any way.

There is another way to prove AFCIs work not subject to contamination by other events. Take similar jurisdictions where one requires AFCIs and the other does not. If the fire stats are different there is your evidence. They are the same for NC and VA as well as IN and MI on a per capita basis.

I didn’t say it prevents shock, I said it prevents electrocution (death).

The AFCI part, I agree with.
 

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
To claim an AFCI trips on anything other than “arcing” is simply not true. During an arc you get a pulsed square-wave looking waveform. This highly nonlinear waveform is what the AFCI is looking for and what it trips on.

I bit off more than I can chew today, and still digesting the simple mechanism that trips AFCI's in Post #52, which me & Don just discovered.

A combination AFCI is as it implies a combined GFCI and AFCI. And in this case I’d agree…it trips in arcing faults and ground faults.

If I hear what you mean in spite of what you say, you can do the same for me.

Perhaps you were confused or your statements were confusing due to your arrogance?

My arrogance is other peoples fault for enabling me, and entertaining my nonsense.

In fact UL, NEC, and manufacturers have been soundly criticized for mandating AFCIs without any simple scientific explanation behind them.

One man's DIY YouTube channel is another man's scientific proof, and I can't argue with deficiencies in critical thinking skills.

Your claim that GFCI does nothing is utter nonsense

Yes, the context was intended to be facetious in my response. One ridiculous turn deserves another.

Ok but surely we can just look at house fires, right?

I am with you on this one.

When other variables occur simultaneously with historical statistics, no single variable gets all the credit.

Small appliance branch circuits for kitchen, dedicated laundry, Disposer/DW, FAU, and much quicker magnetic-trip functions also occurred during the GFCI & AFCI revolutions.

Neither can local regulatory enforcement be ignored as a factor affecting workmanship, building permits, exploit of unskilled labor, or fire-code compliance.

Any statistical approach must prove how all variable affect fire & casualty, before making valid conclusions.

The big claim for AFCIs is something called wood pyrolysis. ..this is actually the mechanism claimed by the CPSC and used as justification for AFCIs.

Some degree of skepticism it's a good thing, which is why you might agree with what we found in post #52

To accuse others of fake news claims when you don’t have a leg to stand on is right up there with most of the things Bob Acosta has to say. With the same level of arrogance and condescension.

Care to try again with actual scientific evidence?

Post #51 summarizes my empirical observation in the field. The only evidence I'm qualified to back up with documented invoices and photos.
 
Location
United States
Occupation
Electrical
A combination AFCI is as it implies a combined GFCI and AFCI. And in this case I’d agree…it trips in arcing faults and ground faults

This is not true. A combination AFCI (CAFCI) breaker by itself provides protection against both parallel and series arcing conditions, it does not imply any ground fault protection. The majority of CAFCI breakers on the market today have no GFCI protection. However a CAFCI breaker used in conjunction with a ground fault receptacle will provide both AFCI and GFCI protection tot he circuit

If you are looking for a breaker that combines AFCI and GFCI protection into one without the needs to a GFCI receptacle, that is called a dual function breaker.

 