Hey guys, happy Friday! I got a chance to get under the hood of the Square D, 3 phase 240v high leg delta panel today. There's a plot twist.
The panel is maxed out with only a couple of slots left open that are the wild leg - I thought I was going to be able to move a couple breakers around but not the case. But below I will explain an easier way but I'm a bit confused (but I'm pretty sure I know what they did here - but want to run it by ya'll).
When I took off the dead front and metered it out, it turns out that C phase is in fact the high leg and is "phased" as PURPLE instead of ORANGE.
I got the usual delta, 3 phase - high leg readings:
- Neutral to A phase = 120V
- Neutral to B phase = 120V
- Neutral to C phase = 208
- A-B-C phase to phase were all 240V between phases
Anyway, I really got a chance to look at the bones of the electrical system at this place and it turns out that this 240v high leg delta panel is feeding another panel with more space in it - it's serving as a sub-panel but I'm confused about the panel rating and how it was metered out.
After taking off the dead front of this other panel that is an Eaton, 3 phase panel, it shows it is a 208Y/120V on the dead front. Below are the readings I got which are the same as the 240V Delta high leg it is being fed from - it is not reading out as 208Y/120V, 3 phase system - here are the reading I got:
So to hook this single phase, 208/230V mini-split HVAC unit up, I can just grab an A&B phase on this Eaton sub panel and get an Eaton 120/240V slash rated, double-pole 40A breaker and call it a day?
I was just surprised to get the readings that I did with this 208Y/120V Eaton panel which resembled the high leg panel.
Main questions here are:
- Can I just grab an A&B phase on this Eaton sub panel and get an Eaton 120/240V slash rated, double-pole 40A breaker and call it a day?
- What are your thoughts about the readings on this 2nd Eaton sub-panel that is rated 208Y/120V but reading out as the high leg, 240V Delta?
We also have a 480V panel. Both the 480V panel and this 208Y/120V Eaton sub-panel are tied into a xformer near all the panels. The xformer ties into the high-leg Delta system which is serving as the "main".
Pics below
Square D, 240V Delta 3 phase high leg panel
Square D, 240V 3 phase high leg "phasing"
Square D, 240V high leg branch circuits
Eaton sub-panel that is being fed with (4) #2's from the Square D, 240V Delta high leg panel
Eaton 3 phase 208Y/120V feeders from the Square D, 240V Delta 3 phase high-leg
Eaton 3phase, 208Y/120V busbar