The issue with slash rated breakers is the withstand capability under fault conditions. Phase to ground faults put the highest physical stress on multi pole breakers, because all of the mechanical forces are exerted onto one pole. So in a slash rated breaker, the ENERGY in the fault is never based on more than 120V, so it has lower mechanical stresses. If there is a fault from the High leg, the energy and stresses will be based on 208V, so the slash rated breaker may not hold together. If there is never a fault, you may never know that the breaker is different. But breakers have to be made for the worst case scenario.