jaggedben
- Northern California
- Solar and Energy Storage Installer
Perhaps I am confused on a couple of things. It appears to me that if I have X current and Y voltage coming from a group of PV panels to get 7.6 kW out of the inverter on 240 and connect the same configuration to 208, I just LOST 1 kW on each converter. Am I confused on that part?
First, as I said already, you wouldn't (necessarily) connect the same group of panels. You would connect fewer panels to the inverter with the lower power rating.
Second, more importantly, the energy you get ultimately depends on the sunshine. Whenever sunshine doesn't reach the inverter power limit, you are losing nothing. See again the thread I posted about clipping. If you connect 1.2kW of PV panels to 1kW of inverter you will typically lose only about 1% of annual energy production to clipping (not 20%).
On the transformer aspect, would a typical 7.6 kW single phase inverter provide one sine wave per 1/60th of a second, or two offset by 120 degrees to match the two phases of the two legs? I would think the same energy loss in combining two phases into one for consumption ((2) 120 legs = 208) would produce further losses as this process is attempted to be reversed, especially if the inverter is only sending one signal per 1/60th of a second.
A typical 240 or 208V grid-tied solar inverter provides a single line-line sine wave, and the transformer it's connected to provides the line-to-neutral voltage and current. Pretty much the same as the utility does on the primary of the transformer.