This question is about sizing the branch circuit breaker for a parking lot lighting system.
I have simplified the numbers for ease of understanding so do not worry if the actual wattages are not correct.
The example is a group of parking lot lights each drawing 1200 watts at 240 volts. We will be connecting them to a Three Phase 240 volt breaker. Each single phase fixture will be connected to the Three Phase feeder in a round robin fasion.( first A,B: Second B,C: Third C,A ect)
I planned to find the maximum number connected to any two legs and use a single phase calculation to determine the circuit amps.
EG. 13 fixtures would give me 5 as the max between any two legs. So I multiply 5 X 1200 and get 6000 then multiply by 1.25 for continous duty and get 7500 then divide by 240 to get 31.25 amps total load.
So I would use a 40 amp breaker, and use the 31.25 amps for VD and other calculations.
Is this correct?
If not, what is the proper way?
I have simplified the numbers for ease of understanding so do not worry if the actual wattages are not correct.
The example is a group of parking lot lights each drawing 1200 watts at 240 volts. We will be connecting them to a Three Phase 240 volt breaker. Each single phase fixture will be connected to the Three Phase feeder in a round robin fasion.( first A,B: Second B,C: Third C,A ect)
I planned to find the maximum number connected to any two legs and use a single phase calculation to determine the circuit amps.
EG. 13 fixtures would give me 5 as the max between any two legs. So I multiply 5 X 1200 and get 6000 then multiply by 1.25 for continous duty and get 7500 then divide by 240 to get 31.25 amps total load.
So I would use a 40 amp breaker, and use the 31.25 amps for VD and other calculations.
Is this correct?
If not, what is the proper way?