rattus said:Stiff, here is another approach:
Compute the highest load current,
Imax = 6000W/240V = 25A
Now assume the other two loads are also 25A, then,
Iline = 1.73 x 25A = 43.3A
Then apply the derating factor,
Ibreaker = 43.3A x 1.25 = 54.1A
Correct for PF if necessary, e.g.,
Ibreaker = 54.1A/0.85 = 63.7A
A bit of overkill perhaps, but we can easily add more load to the other two phases if desired.
Ah, a real world simplified approach, and look Ma, no phase angles!!!