You sure it wasn't two-phase/5-wire?But I have seen a "4-phase" service made this way described in a textbook.
You sure it wasn't two-phase/5-wire?But I have seen a "4-phase" service made this way described in a textbook.
That's what it's called, and that's what it means, but it's really three center-tapped single-phase windings.A typical arrangement is the "hexaphase"
Meaning six phases.
Same discussion, different numbers. I still call it 3-phase, just like the primary.If you look from that centre point to the end of each winding you get six waveforms displaced at 60 degree intervals.
Isn't that six phase?
You sure it wasn't two-phase/5-wire?![]()
Even here.Exactly, but this author called it 4-phase. Goes to show you can't believe everything you read.
In electrical engineering, single-phase electric power refers to the distribution of alternating current electric power using a system in which all the voltages of the supply vary in unison.
I believe we once had a discussion about this and if I remember right, I believe someone showed that with some creative connections, you could run a 3-phase motor from 2-hots and a neutral of a wye system (also being touted as a single-phase service by a lot of posters here).A single-phase supply connected to an alternating current electric motor does not produce a revolving magnetic field.....
Even here.![]()
Some of you smarter guys may want to help the world with better information by getting wikipedia straightened out. From what I read here, their definition of single-phase would not included 120/208 (2 ungrounded and 1 grounded conductors) as a single-phase service.
http://en.wikipedia.org/wiki/Single-phase
I believe we once had a discussion about this and if I remember right, I believe someone showed that with some creative connections, you could run a 3-phase motor from 2-hots and a neutral of a wye system (also being touted as a single-phase service by a lot of posters here).
I'd also like to point out that you cannot take a single-phase service and using transformers create a 3-phase service. PoCo does exactly that whenever they supply a 120/240V Delta 3-phase service.
PoCo does exactly that whenever they supply a 120/240V Delta 3-phase service.
Third item: You have it bassackwards. The POCO takes one phase from one transformer in a 4-wire delta.
If I'm not mistaken, the pump is in the dispenser, and the gas is brought up by vacuum through a dip tube.It's like someone calling the dispenser you use to fill your gas tank a pump when the actual pump is in the underground storage tank.
If I'm not mistaken, the pump is in the dispenser, and the gas is brought up by vacuum through a dip tube.
If the connection was the more common arrangement of the windings at their ends you would have just three voltages at 120deg intervals.Not really. I would argue that the extra "phases" derived through inversions do not count.
It all depends on your point of reference, doesn't it? For example, take a two wire, single phase, 120VAC supply. Connect two (high value) resistors in series from hot to neutral. Connect the ground terminal of your meter to the connection point between the resistors and read the voltages on hot and neutral. You'll see 60VAC on each, 180 degrees out of phase, right? The service hasn't changed, only your reference point has.I say they are.
/QUOTE]
Larry, how can they be in phase when the peaks do not coincide?? To paraphrase K. Y. Tang, "Alternating Current Circuits", two waves are in phase if both waves reach their maximum positive values at the same instant. Clearly, this is NOT the case!
If V1n and V2n were in phase we could safely short them together because there would be zero potential between them. Not even an old hand like Larry would do this on purpose.
Now V1n and Vn2 are in phase, but the discussion centers on V2n!
Good luck. :grin:As I'm laid off I had nothing better to do this afternoon so I think I can settle this once and for all.
The point that there is only one flux in the single-phase transformer was not questioned. The point was that the secondary voltages are exactly the same as the voltages you can get by joining two phase-opposed voltages.Being that there in only one expanding and collapsing electric field from the primary there is no way physically this could cause a lead or lag of a "phase."
No. A phase needs two points (i.e. a voltage).It seems some want to argue that any hot wire constitutes a phase.
It must be defined if you want to use the classic definition of a poly-phase system because there are so many uses of the word "phase"It seems others what to philosophical define what a phase is. That is useless.
And will result in the wrong name for cases where you make phase conversions.The question really is do you define phase order by the primary or the secondary? For all practical purposed and using standard names for systems it seems clearly that defining them by the primary is correct.
I agree with sticking with the conventional names. I'm just proposing that the user understand why the system was named and how it relates to the other possible names.And using the proper names; most anyone in the field should know what you are talking about.
Did anyone say it was not single-phase? I said the voltages can represent both.Question for Sparkys that insist 120/240 is not single phase:
If the nameplate requires 120/240 1PH 60Hz and you have it in your brain that 120/240 has two phases, what kind of phase converter are you going to use?
Hmmm???
:roll: It is about trying to help people understand the common link between poly-phase systems and what appears to be a discontinuity in system definitions. It is because we have an overlap of systems and we have chosen one name above the other.For me I think it just makes sense to call things by their common names and all this 'stuff' about it being single phase or 2 phase amounts to people just trying to prove they have the biggest brains.:roll:
But it is incorrect to say that these voltages are not the same as we would get from using two time-displaced generators.However, it is incorrect to imply that this is a 2-phase system because the extra "phase" is created by a simple inversion--not a second generator.
And that is where we differ. At what point between 90 degrees and 180 degrees does the transformation happen that makes two phases suddenly become one and only one phase?If you took two individual, but synchronized 120v 1ph sources, and connected them "in phase" in such a way that they'd form a 120/240v source, like we get from two 120v windings in series, I'd still call that single phase.
Because that method has flaws. There are 4 L-L voltages in the old 5-wire 2-phase.How about by counting the number of L-L voltages and not the number of L-N ones. After the voltages have been combined the result is a single waveform.
That would go back to your definition of a phase. In the classic sense, the two voltages represent two phases. With the series reference frame, they are two individual phases that remain separate in two individual system classifications. In the neutral reference frame, they are two individual phases grouped into one system classification.I would too! But we can still swap leads and see a phase shift, but not another phase.
What is your definition of phase? Why do you think these waveforms are functionally different in steady-state than the ones you described in #62?Larry, for the 470th time, I am NOT saying there are two phases! I am only saying it is quite proper, even conventional, to express V1n and V2n as phasors with a 180 degree phase difference. There is no rule that one must express V1 and V2 in such a way that they are in phase.
I'm saying the two voltages from the single-phase will be exactly the same as we can get from 180-degree two-phase. They can represent either, but we call them single-phase.The problem my logic has with that is you're saying that a single phase has two phases. I really do grasp what you're saying, of course.
Either reference is a choice. I say both are valid.I dig, but there's no real rule that we must express them in any one way, as far as I know. I understand why we use the grounded conductor, but it's a choice.
No more arbitrary than the other valid choice. In fact, I would say you will find the neutral used as the reference more often.The point (I think) "our side" has been making is that the use of the neutral itself as the focus (right word?) of the vectors is arbitrarily chosen, in the grand scheme of things.
Very nicely put.I know that I am going to need a mortuary licence to keep beating this horse, but the word 'phase' is being used in different ways here.
A single phase service has _two_ phase angles available. The fact that there are two phase angles available does not change that it is a single phase service. The fact that there are two phase angles available does not make it a two phase service.
'Phase' as it applies to service has a meaning that pretty much describes how such a service will be used. You still have a single phase service even if the two supply legs are derived from a wye source, with a 120 degree phase angle difference.
'Phase' as it applies to a sinusoidal waveform has a meaning that simply tells the time displacement of that waveform relative to a reference. Under this meaning, an inversion _is_ a 180 degree phase angle difference. A waveform and its inverse are 180 degrees out of phase. When you look at a waveform and its inverse, you have two phase angles. When you look at Van and Vbn of a _single_ phase service you have _two_ phase angles.
The fact that you have _two_ phase angles when you use the word 'phase' in the phase angle context does not change the fact that you have a _single_ phase service when you use the word 'phase' in the service context.
-Jon
Unfortunately, there are some here that would say that you can't have two phases with a 180 degree separation and you would be forced to have only 3 phases. BTW, I'm not one of those.Are any of you familiar with low voltage high current rectifiers?
A typical arrangement is the "hexaphase"
Meaning six phases.
Typically you have a step down transformer with a three-phase primary. The secondary winding arrangement is star (WYE) but with the windings connected at a centre point rather than the ends. The result looks like six spokes of a wheel. If you look from that centre point to the end of each winding you get six waveforms displaced at 60 degree intervals.
Isn't that six phase?
And I would disagree with you, as would many text books. Some would call the old 5-wire 2-phase a 4-phase system, some would not. I would call it capable of representing both.Not really. I would argue that the extra "phases" derived through inversions do not count.
I think it depends on the context. IEEE calls it 4-phase.Exactly, but this author called it 4-phase. Goes to show you can't believe everything you read.
We call this 2-phase in the utility industry (or "V"-phase).That was very poor wording by me. What I was trying to say is that PoCo (often) takes 2 legs and the neutral of a wye distribution
The utility industry calls it a network service. Probably to distinguish it from the historic 2-phase.then a 120/208 "single-phase" service really is poor wording (and arguable wrong terminology).
But they are forced to call it 3-phase to make their arguments work in the 120/240 or the 5-wire 90-degree cases.Hexaphase has six at 60deg intervals.
So, it is different in that respect.
Correct. A voltage is defined by its reference point and there is no universally "correct" reference point.It all depends on your point of reference, doesn't it? For example, take a two wire, single phase, 120VAC supply. Connect two (high value) resistors in series from hot to neutral. Connect the ground terminal of your meter to the connection point between the resistors and read the voltages on hot and neutral. You'll see 60VAC on each, 180 degrees out of phase, right? The service hasn't changed, only your reference point has.
If you took two individual, but synchronized 120v 1ph sources, and connected them "in phase" in such a way that they'd form a 120/240v source, like we get from two 120v windings in series, I'd still call that single phase.
Because the resemble, as in they measure like, and can be used like they are a single phase. Just as the single, center-tapped secondary resembles two distinct sources that are connected as, measure as, and can be used as a single, center-tapped source.And that is where we differ. At what point between 90 degrees and 180 degrees does the transformation happen that makes two phases suddenly become one and only one phase?
I guess I'm saying that there is no such thing as 180 degrees 2 phase.I'm saying the two voltages from the single-phase will be exactly the same as we can get from 180-degree two-phase.
If I'm not mistaken, we all agree that two individual 1ph transformers (with a single source), a single unit with two individual secondaries, and a unit with one center-tapped secondary (when the first two are connected additively), are electrically identical.They can represent either, but we call them single-phase.