In practice you will find a three phase load of the same KW will require less conductor. This is because ampacity is not linear with conductor size. A three phase load will have smaller conductors, and even though there are 50% more conductors, the total area will still be less. For example consider a 48 KW load. At 240 single phase this would be 200 amps or 3/0 CU, for a total circular mail area of 335600. For three phase that would be 115 amps , #2 CU, for a total circular mail area of 199080. Of course one could theoretically parallel smaller conductors for the single phase case, but there is of course the NEC 1/0 limit for paralleling and even above that in many cases it would not be done.