Single phase vs 3 phase efficiency

Merry Christmas

kwired

Electron manager
Location
NE Nebraska
Occupation
EC
That's not the primary reason; that's just a secondary benefit.

Even if you just look at ampacity, the 3 phase load will require a lower total ampacity of conductors. As 3 (conductors) / sqrt(3) = sqrt(3) < 2 (conductors).

Cheers, Wayne
Which may end up being less copper overall.
 

kwired

Electron manager
Location
NE Nebraska
Occupation
EC
Huh. That is one of those 'I should have known but I didn't know.'

1000W delivered with 2 wires at 480V requires 2.08A. You have to carry 2.08A out and 2.08A back, for a total 'aggregate conductor capacity needed' of 4.16A

1000W delivered with 3 wires at 480V requires 1.2A on each of 3 wires, for a total 'aggregate conductor capacity needed' of 3.61A.

-Jon
Now consider that for most part you will need 14 AWG conductors to comply with NEC in either situation but the three phase application needs three of them instead of two. This isn't as big of an impact on circuits that have smaller conductors to begin with

But then compare the difference with say a circuit that draws 100 amps per line in three phase configuration. You went from 3 -3 AWG for three phase to 2- 2/0 AWG to handle same load at single phase at same voltage. Which is 266200 circular mils vs 108340 in total cross section of the copper portion of conductors. Also need larger raceway to contain the single phase than the three phase conductors.
 

kwired

Electron manager
Location
NE Nebraska
Occupation
EC
Ok so say I have a set of single phase conductors running a load with current X and total power Y. Now I add a third conductor. My total conductor area is now 150% of what it was originally. My power (assuming a reconfigurable load) with the same current X on all three legs is now 173% of Y. Where is that extra capacity coming from? Arnt there extra losses with a third conductor now? :unsure:
If you have a heater assembly with three identical elements all connected in parallel across a single phase source current of supply conductors is 3 times the current of an individual element. Connect them in delta to to a three phase source of same voltage and supply conductors are carrying 1.73 times the current of an individual element - still delivering same power.

If you would happen to connect those three elements in wye instead of delta still delivering same volts you would have less power as there would only be 58% of rated voltage across each individual element in that configuration.
 
If you have a heater assembly with three identical elements all connected in parallel across a single phase source current of supply conductors is 3 times the current of an individual element. Connect them in delta to to a three phase source of same voltage and supply conductors are carrying 1.73 times the current of an individual element - still delivering same power.

If you would happen to connect those three elements in wye instead of delta still delivering same volts you would have less power as there would only be 58% of rated voltage across each individual element in that configuration.
You missed this part of my post, neither one of those situation was what I was saying ;)

assuming a reconfigurable load) with the same current X on all three legs
 

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
Here's a little chart of number of conductors vs power they can carry, where the L-L voltage is limited to some fixed maximum, likewise the current on each conductor is limited. Power values are scaled so the first non-zero entry is 1.

Conductors : Power
1 : 0
2 : 1
3 : sqrt(3) = 1.73
4 : 2
5 : 5 / (2 * cos(18 deg)) = 2.63
2n : n
I tend to think of it in 'electrical degrees'.
Phase Wires​
Electrical Degrees​
Power​
2​
180°​
1​
3​
120°​
1.732​
4​
90°​
1.414​
 

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
I don't think the lower right entry is correct, probably you want "2" there. But maybe you can define what you mean by "power" to confirm.

Cheers, Wayne
Good catch, I was thinking a two phase system would be sqrt 2 like a three phase system is sqrt 3.
But that would only apply for a 3 wire two phase as noted in T430.249. Even then a two phase 3-wire 1.414 would only apply to the 'common' wire of the two phases.
Phase​
Wires (L-L load)​
Watts​
Volts (V)​
Multiplier (M)​
V X M​
Amps per wire​
Single (180°)​
2​
1000​
480​
1​
480​
2.08​
Two (90°)​
3​
1000​
480​
1.414​
678.72​
1.47​
Three (120°)​
3​
1000​
480​
1.732​
831.36​
1.2​
Two (90°)​
4​
1000​
480​
2​
960​
1.04​
 
Last edited:

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
3 phase motors are slightly more efficient than similarly sized single phase motors.

Higher phase counts can provide tiny efficiency improvements, by reducing winding distribution factors and the like.

But the efficiency change is tiny at best.

Jonathan
Looking at the motor tables in the code for compassion of 1 HP 240V motors, assuming PF is equal or negligible there seems to be a pretty big spread of efficiency;

Phase​
Wires (L-L load)​
HP​
VA (V X A)​
L-L Volts (E)​
Voltage Multiplier (M)​
V= (E X M)​
Max Amps per wire​
Single (180°)​
2​
1​
1920​
240​
1​
240​
8​
Three (120°)​
3​
1​
1746​
240​
1.732​
415.68​
4.2​
Two (90°)​
4​
1​
1536​
240​
2​
480​
3.2​
Two (90°)​
3​
1​
1527​
240​
1.414​
339.36​
4.5​
DC​
2​
1​
1128​
240​
1​
1​
4.7​
 
Location
Canada
Occupation
Sales
I had a discussion with a co worker today, say there's a 1000w heater, hooked up to single phase 480v, amp draw would be roughly 2 amps. Now would the same exact heater, hooked to 480v 3 phase have a lesser amp draw? I've heard people say that 3 phase power is 40% more efficient but I don't know how calculate it other than 1000w÷480v.

Sent from my SM-A037U using Tapatalk
Not sure where he got 40%. However, it can be broken down as follows:

1ph 480V you are using a 3 wire system. 3ph 480V you are using a 4 wire system. Basic math, you use 33% more wire in a 3ph system than you would in a 1ph system.

Delivered power in a 1ph system, in basic physics, P=IV.
Delivered power in a 3ph system, in basic physics, P=1.73*IV.

You get 73% more delivered power in a 3PH system.

Hence, for 33% more wire, you get 73% more delivered power using a 3PH system. So, maybe your friend did 73-33 = 40%, which isn't exactly correct but sure whatever.

3Ph becomes more efficient as your loads get increasingly larger. It was first invented for power distribution (in the Gigawatts). I wouldn't get too caught up over a 1kW load. 15kW and up, start looking into it.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
Not sure where he got 40%. However, it can be broken down as follows:

1ph 480V you are using a 3 wire system. 3ph 480V you are using a 4 wire system. Basic math, you use 33% more wire in a 3ph system than you would in a 1ph system.

Delivered power in a 1ph system, in basic physics, P=IV.
Delivered power in a 3ph system, in basic physics, P=1.73*IV.

You get 73% more delivered power in a 3PH system.

Hence, for 33% more wire, you get 73% more delivered power using a 3PH system. So, maybe your friend did 73-33 = 40%, which isn't exactly correct but sure whatever.

3Ph becomes more efficient as your loads get increasingly larger. It was first invented for power distribution (in the Gigawatts). I wouldn't get too caught up over a 1kW load. 15kW and up, start looking into it.
To be CLEAR though, lower amps through the conductors is NOT less power! 1000W is still 1000W regardless of how it gets delivered. So there is no significant difference in efficiency. The only difference is maybe a slightly lower I2R (resistance) losses in the conductors in that for the SAME kW LOAD IN THE SAME SIZE CONDUCTORS, the lower conductor heating will result in a tiny reduction of energy losses in the wires.
 

kwired

Electron manager
Location
NE Nebraska
Occupation
EC
Not sure where he got 40%. However, it can be broken down as follows:

1ph 480V you are using a 3 wire system. 3ph 480V you are using a 4 wire system. Basic math, you use 33% more wire in a 3ph system than you would in a 1ph system.

Delivered power in a 1ph system, in basic physics, P=IV.
Delivered power in a 3ph system, in basic physics, P=1.73*IV.

You get 73% more delivered power in a 3PH system.

Hence, for 33% more wire, you get 73% more delivered power using a 3PH system. So, maybe your friend did 73-33 = 40%, which isn't exactly correct but sure whatever.

3Ph becomes more efficient as your loads get increasingly larger. It was first invented for power distribution (in the Gigawatts). I wouldn't get too caught up over a 1kW load. 15kW and up, start looking into it.
It is a little more complicated than that.

Lighter loads you maybe don't gain a lot of advantage when it comes to how much copper is needed to supply same load. What I 'm getting at here is if you can run say 14 AWG either way, then you use less copper for same load on a single phase circuit. But if you can add one conductor but reduce size of all three by that 1.73 factor then you do use less copper for same power at three phase and same volts.

If you step up from 240 single phase to 480 three phase you go from needing a pair of 6 AWG conductors for say a 10 HP motor to being able to use three 14 AWG conductors, but you will likely have more expensive motor controller, breakers, etc. to consider as well. If it is something that doesn't get a lot of use, approximate watt hours will be same either way and up front costs may become even more significant
 
Location
Canada
Occupation
Sales
It is a little more complicated than that.

Lighter loads you maybe don't gain a lot of advantage when it comes to how much copper is needed to supply same load. What I 'm getting at here is if you can run say 14 AWG either way, then you use less copper for same load on a single phase circuit. But if you can add one conductor but reduce size of all three by that 1.73 factor then you do use less copper for same power at three phase and same volts.

If you step up from 240 single phase to 480 three phase you go from needing a pair of 6 AWG conductors for say a 10 HP motor to being able to use three 14 AWG conductors, but you will likely have more expensive motor controller, breakers, etc. to consider as well. If it is something that doesn't get a lot of use, approximate watt hours will be same either way and up front costs may become even more significant
I think you missed the last part of my post.
 
Location
Canada
Occupation
Sales
To be CLEAR though, lower amps through the conductors is NOT less power! 1000W is still 1000W regardless of how it gets delivered. So there is no significant difference in efficiency. The only difference is maybe a slightly lower I2R (resistance) losses in the conductors in that for the SAME kW LOAD IN THE SAME SIZE CONDUCTORS, the lower conductor heating will result in a tiny reduction of energy losses in the wires.
I think you missed the point of my post. Thanks for clearing up what I may have not specified. Yes 1000W is still 1000W
 