What is the specif theory behind why we refer to 2 poles as single phase?
My oversimplified answer is because it comes from one phase of the utility power.
for a common 120/240 delta It goes into a transformer and they give opposite sides of that single phase. the null point in the windings is the neutral.
As far as you panel is concerned you have 2 phases.
I imagine they do this because it is much cheaper to run single power lines all though out an area.
On a system where there is no primary neutral, the transformer is wired phase to phase, making it really a two phase source.
It may be a two pole source, but still only one phase.
The utillity usually does only supply one phase and neutral...
Are you using the term Phase to describe a single physical conductor?
I have noticed that 'Utility industry' terminology is often different than IEEE/ANSI terminology, especially when it comes to describing voltage systems (e.g. using LV/HV versus HV/LV based on the system).
.... On a three phase three wire system, the circuit is between any two PHASES.
My oversimplified answer is because it comes from one phase of the utility power.
I like that answer best myself, but beware this very topic has turned into threads hundreds of posts long just on debate over the definition of "phase".Charlie gave the answer that I was looking for, but thank you all for your input.
You kind of said it in your post there - "pulled from two phase conductors"I understand what was said above, but our line crews
call a two insulator (high side) two phase in the areas
where there is only three phase delta. Yes it could be
considered wrong but it is only semantics. If they get
it wired up right for our customers that's all that really
matters any way.
In my time I've been on both sides of this fence as to
what to call the high side when pulled from two of the
phase conductors, but on the other side of the transformer
it is still the 120/240v single phase system we would get
from one primary phase and the grounded system neutral.
Both installations are right and are reliable.
(Just my opinion)
JR
The scope needs the ability to connect to more then two leads as well or you will still only see one wave on the scopeI grew up with all three, Single phase, Two phase, and Three phase.
When you look at them on a scope you will only see one sign wave for a single
phase system, it is referenced to ground so you get a positive RMS phase to
ground readind, a negative RMS phase to ground reading, or a positive to negative
RMS reading.
On a two phase system ( it was 5 wire I think, don't know if they are still used, most people never
heard of it) A scope shows two sign waves 180 degrees out of phase. And on a
three phase system you have 3 sign waves 120 degrees out of phase. Resolvers use two phase, 90 degrees out of phase
So if someone says two phase it is a sure bet they mean single phase. Bet them
it does not have two phases on a scope.