electricalist
Senior Member
- Location
- dallas tx
I love when a customer asks this very question. After reading all the answers I feel much more comfortable saying I have no clue.
I often know the answer to customer questions but never know how to explain in a manner that they will understand, or if I do - they will forget it in a very short time anyway. GFCI and AFCI are about the worst thing to explain why we need them to a non electrician and worse yet to someone that does have a little understanding of electricity as they think they are just a simple circuit breaker of some sort, and they always ask why we can't just depend on the breaker back at the panel?I love when a customer asks this very question. After reading all the answers I feel much more comfortable saying I have no clue.
Yep, sorry. You are right. I keep forgetting that. I've never actually WORKED on a 2 phase system, I've only dealt with it from afar and had to learn about it after the fact and that first encounter was described to me as having a 180 degree phase shift, so my brain keeps getting stuck there. Someone corrected me like you just did, but it's so rare that i forget again.We do not usually consider a 180 degree phase shift as a second phase since it can be derived by a transformer. Legacy two phase in the US has a 90 degree separation.
It often (always?) consists of four wires plus a neutral so that the phase angles are 0, 90, 180, and 270. But we do not call it four phase for the same reason that we do not call 120/240 three wire "two phase".
They originally were called quarter-phase systems and were noted as being correctly called a four-phase system. It was only the usage that made people accustomed to calling it a two-phase system. A 3-wire 90 degree two-phase system is still recognized as part of a four-phase system. Six-phase systems are recognized in the same manner. Nothing new, this has been the case since the turn of the 20th century.It often (always?) consists of four wires plus a neutral so that the phase angles are 0, 90, 180, and 270. But we do not call it four phase
They originally were called quarter-phase systems and were noted as being correctly called a four-phase system. It was only the usage that made people accustomed to calling it a two-phase system. A 3-wire 90 degree two-phase system is still recognized as part of a four-phase system. Six-phase systems are recognized in the same manner. Nothing new, this has been the case since the turn of the 20th century.
With the vector diagram included, that is one of the best explanations of how a Scott T configuration works that i have seen.A Scott transformer.
A Scott transformer.
I guess they might get confused but then one would have to question their proficiency with an oscilloscope.Sorry it?s UK voltages.
If you put an oscilloscope on the two phases you will get a single sine wave, a dual trace oscilloscope connected between Ph-N-Ph will give opposing sine waves. An awful lot of confusion comes from this. Some will say the O/P is 180? opposed but the windings are at 0? if they were at 180? you can see what happens. Not a great deal of use.
Square D has taken a step in that direction with the dual function AFCI - GFCI circuit breakers, I imagine others will eventually have something similar. I don't see the simple single pole breaker disappearing from the market either though- until codes make it unneeded anyway.There are many international ciruit breakers that look like a 2 pole device but are really 1 OCPD and 1 switch. This is similar to our "switched neutral" breakers except the grounded conductor plugs on to the busbar.
On single phase 220vac, you have 2 "hot" wires that each test at 120v to ground but 240v from one to another. Each side can act independently as a 110-120 leg but the two of them are 180 degrees out of phase with one another, allowing them to essentially act as a team.
Good spot for an ungrounded_Y-Y with a delta tertiary.On the subject of phase shifting, I inherited this little beauty when I changed companies.
Good spot for an ungrounded_Y-Y with a delta tertiary.
On the subject of phase shifting, I inherited this little beauty when I changed companies.
![]()
It should be. That was the issue.Wouldn't the transformer on the left be different from the right?