Wouldn't the transformer on the left be different from the right?
The phase angle was 30o advanced. It shows it at the bottom of the drawing.
Wouldn't the transformer on the left be different from the right?
The phase angle was 30o advanced. It shows it at the bottom of the drawing.
After reading through all of the answers I wonder...
Why is a degree called a degree? :angel:
I may be wrong, but I think it comes from phase angle which is referred to sometimes as degrees? I wonder too.
Different degrees of sarcasm.:angel:I guess I wasn't sarcastic enough...:slaphead:
After reading through all of the answers I wonder...
Why is a degree called a degree? :angel:
I guess I wasn't sarcastic enough...:slaphead:
Thanks!
So, correct me if I am wrong, but in theory I could do this:
11kv buss with 2 feeders:
For feeder 1.
Yd11 11 to 3.3kv trafo
Dyn01 3.3kv to 433 volt trafo
For feeder 2.
Yyn0 11kv to 400 volt trafo
Both 400 volt secondaries can be paralleled because the vector groups in the end match zero degree of phase shift.