Which the inspector wants change to single PlexI have two separate 20 amp circuits with two separate 20 amp rated duplex receptacles
Only if they have adopted and published amendments to the NEC. They must be officially adopted by the unit of government that adopted the code.It could be their own code. AHJ overides NEC. I think the receptacle can be made half hot, though, which is what I always see, with dw plugged into constant side. Specs is another place to look.
Sent from my SM-N910V using Tapatalk
It could be their own code. AHJ overides NEC....
I wish more people understood that
I'm still in my apprenticeship, but this occured to me early on. If I'm correct, cities/jurisdictions choose what codes they adopt. NEC isn't an authority like OSHA. (I could be wrong on this, and would appreciate corrective feed back) So, just quoting code isn't the end of the argument. I think the better angle is arguing how the function of your install satisfies the concerns of his requirements.I wish more people understood that
I'm still in my apprenticeship, but this occured to me early on. If I'm correct, cities/jurisdictions choose what codes they adopt. NEC isn't an authority like OSHA. (I could be wrong on this, and would appreciate corrective feed back) So, just quoting code isn't the end of the argument. I think the better angle is arguing how the function of your install satisfies the concerns of his requirements.
Sent from my SM-N910V using Tapatalk
Thx. That's exactly what I thought.Yes the NEC is not an authority, it is a model code that jurisdictions can adopt as is or with amendments.
Once a code is adopted by a governing body it becomes law.
An inspector, like a police officer, can only enforce adopted law.
Thx. That's exactly what I thought.
Sent from my SM-N910V using Tapatalk
And, so, my answer was simply that he needs to make sure what the inspector is referencing for this requirement. Because the answer may be outside of what he knows of the NEC.So unless the inspector can show an adopted section for simplex receptacles in the OPs case, it is not required and unenforceable.
210.21(B) Receptacles.
(1) Single Receptacle on an Individual Branch Circuit.
A single receptacle installed on an individual branch circuit
shall have an ampere rating not less than that of the branch
circuit.
Exception No. 1: A receptacle installed in accordance
with 430.81(B).
Exception No. 2: A receptacle installed exclusively for the
use of a cord-and-plug-connected arc welder shall be permitted
to have an ampere rating not less than the minimum
branch-circuit conductor ampacity determined by 630.11(A)
for arc welders.
But a duplex receptacle is not a single receptacle.Is that one 20 amp cir on each unit? If so,
Inspector is requiring single receptacles, not duplex, for DW and disposal. Is this required by NEC?
Is this so someone will not plug in an instant hot water heater under the sink?
Where are you located? In the Mass amendments there is an additional paragraph in 210.21(B).
"Receptacles on Individual Branch Circuits A receptacle outlet installed to comply with a requirement for an individual branch circuit shall contain a single receptacle, or multiple receptacle if, and then only to the extent that, the supplied equipment includes multiple supply cord connections."
So, IF the equipment requires a dedicated circuit, it needs a single receptacle, otherwise a duplex is OK.