Actually the microwave range hood is required to have a single receptacle especially if the unit calls for a separate circuit. A duplex would allow something else to be plugged in and then 210.23 could applyNothing in the NEC requires single outlets for the locations you have specified.
PeterOK, I concede the code requires it in this instance. But in reality, is a receptacle that's 5' off the floor inside of a small cabinet (most of the time) in any real danger of having something else plugged into it? I know, I'm arguing about a receptacle that costs $3.
If it truly is a dedicated circuit you may need a single receptacle. The fridge "could be" a dedicated 15 amp ckt, but oftentimes it is a 20 amp, either dedicated or off the counter top receptacles. The laundry outlet doesn't need to be dedicated, it can serve other outlets in the laundry, (not the lighting). You might have a duplex with the washer plugged in and the gas dryer. Some posters here have suggested the "single receptacle option" is obsolete, like using a single receptacle instead of a gfci for say the dishwasher or sump pump.I did read the articles you mentioned and I couldn't find exactly where it says microwaves need a single receptacle. Also if it is mandatory why aren't other single appliances that have a dedicated circuit required to have single receptacles like a refrigerator and washing machine. Any thought? Thank you again
210.23(A)(2) Utilization Equipment Fastened in Place. The total
rating of utilization equipment fastened in place, other than
luminaires, shall not exceed 50 percent of the branchcircuit
ampere rating where lighting units, cord-and-plugconnected
utilization equipment not fastened in place, or
both, are also supplied.