jaggedben
Senior Member
- Location
- Northern California
- Occupation
- Solar and Energy Storage Installer
Looking at 230.71 again, the matter doesn't hinge on whether they are service entrance conductors or not. It's simply that the exceptions in 230.40 are the only way to have more than six total disconnects for any service.
Otherwise the only way that you could feed (8) disconnects on separate buildings are if the utility owns the (8) sets of conductors so that it's technically (8) separate services.
Otherwise the only way that you could feed (8) disconnects on separate buildings are if the utility owns the (8) sets of conductors so that it's technically (8) separate services.