- Location
- Lockport, IL
- Occupation
- Semi-Retired Electrical Engineer
Thanks. That was what I was thinking about.hmspe said:In Sight From (Within Sight From, Within Sight). Where this Code specifies that one equipment shall be "in sight from,'' "within sight from,'' or "within sight,'' and so forth, of another equipment, the specified equipment is to be visible and not more than 15 m (50 ft) distant from the other.
You are right, 225.32 does not use the phrase “in sight of.”hmspe said:225.32 doesn't use or imply any of the terms listed.
The rule is “readily accessible and nearest the point of entrance.” The rule allows us to put the disconnect outside the building, but it does not say the disconnect must be attached to the building. So how far outside is acceptable? That is a matter for the AHJ to decide.hmspe said:50' away doesn't seem to qualify as "nearest".