The requirement for a single main disconnecting means will enhance the safety of facilities. The six disconnect rule 230.71 (A) creates many problems for Electricians and Engineers in adding new electrical power distribution for new loads in an existing facility. A single main disconnect allows for the addition of new feeder devices without having to re-configure the service. Also, the single main disconnect is far safer as it allows the First Responder/Fire Department personnel or Electrician to easily disconnect power to the entire facility. Also, the new 2017 UL 67 Requirement for New Service Entrance Panelboards (NEC Article 408.3 (A)(2) requires that with the service disconnect in the off position, no ungrounded uninsulated live part is to be exposed to inadvertent contact by persons while servicing any load terminal, including a neutral load terminal, a branch circuit equipment grounding terminal, or the neutral disconnect link. The six handle rule has been used to avoid compliance with the GFCI protection for main disconnects of 1000 Amps or higher (230.95)
I cant see a single disconnecting means enhancing the safety of a facility.
Yes the 6 disconnect rule does hinder adding new loads if you're already at a max of 6 movements.
A single main does not allow for the addition of new feeder devices if the services is not built to handle the additional load in the first place.
I would agree the single main is a quicker way to disconnect power from a structure in case of an emergency.
Yes a main that is off may reduce a hazard on the load side of it, but, the hazard, or inadvertent contact still remains inside the panel on the line side so that is nothing more than a false sense of security.
I don't know of anyone who would service a load terminal or a neutral disconnect link without shutting the power off anyway.
Never really thought about using the 6 disconnect rule to avoid compliance with GFI protection, but, why is that not a genius way of thinking?
NEC made the rule on the 1000 amp and above rule to begin with. If they didn't want that rule bypassed they should have lowered the amperage requirement on services above 240 volts.
Point is, the panel should actually be completely shut down if working inside of it.
Just my 2 cents worth.
JAP>