Size of Service Disconnect

Status
Not open for further replies.

5Spot

Member
I've got a new office building going up with 8 office spaces for tenant improvement. Each office space has a calculated load of 87 amps. I'll be providing 100 amp sub panels at 120/208, 3 phase for each office. For my switch gear, how do I calculate the size of the main service disconnect feeding all 8 panels? The power company is providing 120/208, 3 phase to the building?
 
Do you have an operating load????????If not I think this is a spot for a SWAG of .5 diversity,in the absense of no direction from client,that would give you roughly a 400 amp disconnect. It will be interesting to see others approach.I would size the wire for nearly max connected in case you start getting nuisance trips and then you could simply upgrade your trip or fusing protection as needed.

dick
 
Last edited:
A/C and lighting are figured at 100%. Article 220 gives you a reduced demand factor for receptacles and kitchen equipment if you have any. SWAG factors are not listed.
 