This is a multifamily building project with modular apt units. Each apt unit is delivered to the site from the factory as a module. It has a 4#2/0 & 1#1G AL SER Cable whip. We need to make connections between the SER cable from the modular unit to the 4#2/0 & 1#1G AL MC Cable from the building electrical panel.
As an engineer I am not very familiar with junction box sizing which is usually done by electricians. I sized the junction box as below, could you let us know your thoughts on the required junction box dimensions.
A. If the cable enters from the sides, and not leaving the box from opposite wall (i.e. angle pull or U-pull), according to NEC 314.28:
1. Transposing the 4#2/0 AL & 1#1 AL GND SER cable size into raceway size, the minimum required trade size raceway for the conductors in the cable is 2".
2. For angle pull or U-pull that cable entering from sides (not entering the box opposite the removable cover), it doesn't fall under the exception in 314.28 (2). So you can not use table 312.6(A). The box shall not be less than 6 x 2" = 12" as per 314.28 (2).
The minimum required junction box is 12" x 12" according to NEC 314.28.
B. If the cable enters from the back (entering the box opposite the removable cover) and leaves from the sides, you can apply NEC table 312.6(A). The minimum required bending space for 2/0 AL SER cable is 3" (from end of connector to the wall). Adding the connector dimensions, a 10" x 10" x 6" box maybe enough.
But I can not source a 10" x 10" x 6" box with factory installed knockouts on the back. All products I search online only have knockouts on the sides. Is this an adaptive that the manufacture typical can make for you?
Or can you make the hole at the back by yourself? Is it an easy work for example to the junction box attached? They need 300+ of these boxes.
As an engineer I am not very familiar with junction box sizing which is usually done by electricians. I sized the junction box as below, could you let us know your thoughts on the required junction box dimensions.
A. If the cable enters from the sides, and not leaving the box from opposite wall (i.e. angle pull or U-pull), according to NEC 314.28:
1. Transposing the 4#2/0 AL & 1#1 AL GND SER cable size into raceway size, the minimum required trade size raceway for the conductors in the cable is 2".
2. For angle pull or U-pull that cable entering from sides (not entering the box opposite the removable cover), it doesn't fall under the exception in 314.28 (2). So you can not use table 312.6(A). The box shall not be less than 6 x 2" = 12" as per 314.28 (2).
The minimum required junction box is 12" x 12" according to NEC 314.28.
B. If the cable enters from the back (entering the box opposite the removable cover) and leaves from the sides, you can apply NEC table 312.6(A). The minimum required bending space for 2/0 AL SER cable is 3" (from end of connector to the wall). Adding the connector dimensions, a 10" x 10" x 6" box maybe enough.
But I can not source a 10" x 10" x 6" box with factory installed knockouts on the back. All products I search online only have knockouts on the sides. Is this an adaptive that the manufacture typical can make for you?
Or can you make the hole at the back by yourself? Is it an easy work for example to the junction box attached? They need 300+ of these boxes.