wwhitney
Senior Member
- Location
- Berkeley, CA
- Occupation
- Retired
I'm not saying that 430.62 requires you to use a 35A OCPD, I'm saying that when you do the computation, based on the information given so far, the possible outcomes are 30A max, 35A max, or 40A max. [I originally thought 30A max was not possible, but reviewing the algebra it is, although unlikely.]I don't see how, when the language clearly says "having a rating or setting not greater than".
Then I'm further saying that when larger than 30A is allowed, choosing to use 30A would be like using a 20A or 25A OCPD on the branch circuit for the 18.9 MCA / 30 MOCP unit. Which is allowed, but often here I see the attitude "just use the MOCP, it's allowed and is least likely to nuisance trip."
That's all I was saying about 430.62. I'm more interested in 430.63 and how to interpret it, and 430.63 would apply if either unit includes a non-motor load. 430.63 also includes the language "not less than" rather than "not greater than."
Cheers, Wayne