wwhitney
- Berkeley, CA
- Retired
430.62 says to start with the "largest rating or setting of the branch circuit short-circuit and ground-fault protective device for any motor supplied by the feeder" and further clarifies "based on the maximum permitted value for the specific type of a protective device in accordance with 430.52, or 440.22(A) for hermetic refrigerant motor-compressors".Now I'm trying to compute the feeder size based on 430.62
440.22 says to use the branch-circuit selection current, which will be on the nameplate (and is equal to the Rated Load Current if not separately specified on the nameplate), so we don't need to use the tables in 430 for hermetic refrigerant motor-compressors. But you are correct that if the largest motor is not a hermetic refrigerant motor-compressor, then 430.6 tells us to use the table FLC based on HP, rather than the nameplate FLC, for this part of the calculation.
One thing I'm not certain about is that 430.62 then says to add "the sum of the full-load currents of the other motors of the group;" is that the nameplate FLCs or the tables FLCs? 430.6 says to use the table values for determining "the ampacity of conductors or ampere ratings of switches, (and) branch-circuit short-circuit and ground-fault protection," but 430.62 is about determining the feeder SCGF protection, not the branch-circuit SCGF. So I think for this part of the computation we do use the nameplate values, rather than the table values.
Cheers, Wayne