I need to wire a temp . 480v AHU package unit and only have 120/208. Can I use a buck boost transformer? Where do I find the formula for sizing? Tia!
Absolutely.No. Use a step up transformer.
Ok so using a step up transformer should I use a 208 delta to 480/277 wye? And the Ahu has 60amp MOP. As of now I have only a 100 amp breaker on a bus duct. Would I be correct at determining the amps at 208/480=.433x100= 43.3 amps, so I would need a larger breaker? And what formula would I use to size the step up transformer? Been awhile since dealing with transformers but I learn really fast so thanks for the help guys!No. Use a step up transformer.
Usually current * the change in voltage, I believe
50 * 272 = 13600 and not sure if you would need three or not. Never attempted it.
Why two step up transformers?you can do this with two stepup xfmrs.
Ok so using a step up transformer should I use a 208 delta to 480/277 wye? And the Ahu has 60amp MOP. As of now I have only a 100 amp breaker on a bus duct. Would I be correct at determining the amps at 208/480=.433x100= 43.3 amps, so I would need a larger breaker? And what formula would I use to size the step up transformer? Been awhile since dealing with transformers but I learn really fast so thanks for the help guys!Absolutely.
two single phase step-up xfmrs used as an autotransformer bank. the transformer company should have a wiring diagram.Why two step up transformers?
Mca is 49 ampsAt best, you have a tight situation. Once you know the MCA you can get a better idea,
At 60 MOCP you are possibly looking at a MCA of 45 or so or 38 kw on 480.
A 45 kva transformer will have a primary current of 125 amps on 208 so your 100 amp buss breaker will be marginal at best.
When you consider inrush currents on the HVAC and the transformer, IMO, a 100 amp buss breaker and 45 kva transformer is risky.
MCA is 49ampsIMHO the ideal transformer for this job is a 208V delta to 480/277V wye step up transformer. Probably 45 or 75 kVA.
The current at 208V must be greater than the current at 480V, so you are correct, 100A at 208V is the equivalent of of about 43A at 480V.
This might _barely_ be sufficient to run the AHU, the MOP (maximum overcurrent protection) of the AHU is certainly greater than the operating current. Does the AHU have an MCA (minimum circuit ampacity) rating?
Regarding using 2 single phase step up transformers...this is one of the possible autotransformer arrangements which could be made to work. My recommendation is to avoid this unless you already have suitable transformers.
The only autotransformer setup that I would consider is a packaged wye 3 phase autotransformer. This gets you something which can take any input (208, 240, 400, 480, 600) and give you any of the others as output...but depending upon the situation might require a primary neutral brought to the transformer. Might be a better choice for a temporary install because it gives you a tool that has value elsewhere. For example:
I have no experience with the autotransformer linked.
Jon
Many good answers, but a thought. Many (most?) 480 systems can be connected for 240, PERHAPS 208. Have you contacted the manufacturer?I need to wire a temp . 480v AHU package unit and only have 120/208. Can I use a buck boost transformer? Where do I find the formula for sizing? Tia!
Wasn't thinking clearly I'll be sizing the secondary to the 60 MOP. Thanks for the input haven't found the calculation yet to see if 45kva would suffice though.With all the engineering factors involved I certainly am not qualified to size the transformer but a SWAG I;'d think at 49 MCA a 45 kva would suffice but hopefully better qualified folks will chime in.
You secondary conductors, IMO, would need to be rated at 49 amps to meet the MCA.
(FWIW I'd feed the transformer with a 150 amp OCO at the buss)
No it would usually say on nameplate if it could run on 208v I'll double check from the manufacturer but I'm sure it will not! Thanks for the input. Great advice!Many good answers, but a thought. Many (most?) 480 systems can be connected for 240, PERHAPS 208. Have you contacted the manufacturer?