Show your math and then I will help.
1.732 x 49 amps x 480v= 40,736.64Show your math and then I will help.
Update: Ok I do have a 200amp source off the bus duct. Now should i have a 45kva or 75 kva transformer and need to find size of wire for secondary side to the AHU. MOP IS 60 MCA is 49
No it would usually say on nameplate if it could run on 208v I'll double check from the manufacturer but I'm sure it will not! Thanks for the input. Great advice!
there is not enough difference in cost between a 45 and a 75 kVA transformer to matter much. That extra cost is dwarfed by the labor costs.It's a shame standard 3 phase transformer sizes jump from 45 to 75.
IF I was doing the install, I would install the 45 but, as noted, you do need to be aware there is a possibility of inrush problems.
(In the event of an in-rush problem, a HVAC soft-start might eliminate the problem)
The compressors were not 208 compatible or at least the name plate did not list 208 as an optionIt also may be internally wired for 208V but designed to be easily connected for 480V
10’s, 15’s then 25’s...It's a shame standard 3 phase transformer sizes jump from 45 to 75.
IF I was doing the install, I would install the 45 but, as noted, you do need to be aware there is a possibility of inrush problems.
(In the event of an in-rush problem, a HVAC soft-start might eliminate the problem)
You have a 3 phase 480 to 240 step down?Update so I got a s step down 75 kva transformer and gonna wire in reverse. After alot of studying the consensus was to disconnect the bonding jumper but not sure why. Has anyone wired a transformer in reverse and can you tell me why we would not want it bonded?
Yes and plan on wiring it in reverseYou have a 3 phase 480 to 240 step down?
A step down used in reverse is really not a good idea. Try and get the correct transformer.Update so I got a s step down 75 kva transformer and gonna wire in reverse. After alot of studying the consensus was to disconnect the bonding jumper but not sure why. Has anyone wired a transformer in reverse and can you tell me why we would not want it bonded?
common practice for years but only allowable by NEC if approved by manufacturerYes and plan on wiring it in reverse
Cannot get a step up. Do you know of any specific reason why its not a good idea?A step down used in reverse is really not a good idea. Try and get the correct transformer.
IMO 45KVA is fine. Typically, actual running current is 66% of MCA. A 75 KVA is $100 more in no load losses per year....
Why not? That is a super common transformer.Cannot get a step up. Do you know of any specific reason why its not a good idea?
I asked for a 208delta/480wye step up and senior project manager got me a used step down and says to wire it in reverse. Did as much research as I can up to this point and seems most electricians are divided on it's a bad idea and that yeah it works the same in reverse just disconnect the bonding jumper at xo and I will have no neutral.Why not? That is a super common transformer.