When using ground rods as a grounding electrodes, how do you size the conductor to use?
When the designer specifies them, if they so choose or when it is a "pipe" electrode. See below:and when are 3/4" ground rods required?
so I does no matter the size of the service. Even a 400 amps , only requires a #6 wire, right?
so I does no matter the size of the service. Even a 400 amps , only requires a #6 wire, right?
Table 250.66
Well lets not actually call them exceptions fella...Actually its section 250.66, as the section gives exemptions to the sizes in Table 250.66, take a look at 250.66(A) for your answer
Well lets not actually call them exceptions fella...*grin*...we on that panel like to call them permitted applications inlieu of the general rule.
Paul W. Abernathy
Electrical Code Academy, Inc.
CMP #5 and #17
Snap...never thought of them that way. My appologiesFor the record he called them exemptions.![]()
My bad Tom....sorry fellaActually its section 250.66, as the section gives exemptions to the sizes in Table 250.66, take a look at 250.66(A) for your answer