Sizing KVA of Transformer

Status
Not open for further replies.

LibertyEngineering

Senior Member
Location
Allentown, PA
I know someone on this forum can break this down for me.



Making this simple , here is what I am trying to get a better handle on.



I am told I have (100) 5 HP motors All 208/3PH. Each motor is 3.8KW., .8 PF



Selecting a transformer size to properly feed these motors



3.8 x 100 = 380KW



Now do I divide this by .8 for transformer size?



380 / .8 = 475 so a 500KVA transformer.





Thanks for the reply.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
You need to create a loading profile.

Will all of your motors be fully loaded at the same time?
Are the motors controlled by a VFD?
How many of the motors start at one time? Do some motors start while other motors are running? How long does it take for the motors to finish accelerating?
 

LibertyEngineering

Senior Member
Location
Allentown, PA
You need to create a loading profile.

Will all of your motors be fully loaded at the same time?
Are the motors controlled by a VFD?
How many of the motors start at one time? Do some motors start while other motors are running? How long does it take for the motors to finish accelerating?

Yes of course.
Motor Duty factor is already included in the total KW
All motors on VFD's or RVS's
Motors will start intermittently
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Yes of course.
Motor Duty factor is already included in the total KW
All motors on VFD's or RVS's
Motors will start intermittently

I mean a true loading profile.
100 motors running variable torque load at 50% capacity on VFDs, with 10 motor starting and stopping occasionally, is a different load profile than 100 motors running constant torque loads at 100% capacity with 50 of them starting and restarting every 10 minutes using an RVS with a 30sec acceleration time.
 

topgone

Senior Member
Yes of course.
Motor Duty factor is already included in the total KW
All motors on VFD's or RVS's
Motors will start intermittently
The idea suggested by the poster above is the loading profile that most likely describe how your loads behave.
  • Some motors are interlocked with another motor or
  • motors are required to be run simultaneously, or
  • the load will only run on emergencies, or
  • there are loads that act as backup equipment (redundant unit) should the running unit drop off, etc.
You will end up with a very big transformer if you just add the loads and plug in a fudge factor for future loads, IMHO.
 

paulengr

Senior Member
Lots of issues here. The VFD will nullify the power factor if it’s an AFE or not if it’s diode front end. Need the VFD pF. Also the VFDs will consume power so you need their name plates. As already mentioned if you start and accelerate real slow with a max of 100% FLA on variable torque loads only (fans, centrifugal pumps) then you can size at just 380 / 0.95 or 400 kva. In fact that may be very realistic depending on actual load. If it’s all conveyors all starting and accelerating at say 150% of FLA at the same time you’d need at least 400 x 150% or 600 kVA. You might be able to take into account some acceptable voltage drop though and trim it a little.

Also another major concern here is short circuit. Chances are highly likely that if you put more than 10 VFDs on one transformer you will need to either use lube reactors on every one or semiconductor fuses. This will seriously blow up your budget. You will probably find it’s far more economical to put say 8 VFDs per transformer and run a lot of smaller transformers.

Finally why did you pick the lowest voltage? Those motors are most likely all going to be 9 or 12 lead. So 460 is “free”. You can run smaller VFD, cheaper transformer, cheaper smaller fuses etc.
 

LibertyEngineering

Senior Member
Location
Allentown, PA
The idea suggested by the poster above is the loading profile that most likely describe how your loads behave.
  • Some motors are interlocked with another motor or
  • motors are required to be run simultaneously, or
  • the load will only run on emergencies, or
  • there are loads that act as backup equipment (redundant unit) should the running unit drop off, etc.
You will end up with a very big transformer if you just add the loads and plug in a fudge factor for future loads, IMHO
Well honestly this is not an untypical situation where as the designer we get very little information to complete a project. The above is an example I was applying to a waste water treatment plant but I tried to keep it simple in my question. I understand the concept of what jim dungar is asking but that is information we never will receive before designing the service size for the building because honestly I do not know if there is anyway to know for sure how the motors will operate together. What they did provide was a spreadsheet list of motors with their HP and the KW rating (using 746W per HP) plus a column indicating the duty cycle either 100% or 50%. The majority of the motors we listed as 100% duty cycle. I understand we could end up with a transformer much larger than needed but since the actual usage of the motors is not known beyond the duty cycle of each motor we must design around worst case scenario. What I was merely looking to ascertain is if my thinking is correct in converting the total kW of motor load into a kVA size of a transformer. This is the utility transfomer feeding the service to the building.
 

LibertyEngineering

Senior Member
Location
Allentown, PA
Finally why did you pick the lowest voltage? Those motors are most likely all going to be 9 or 12 lead. So 460 is “free”. You can run smaller VFD, cheaper transformer, cheaper smaller fuses etc.
Actual they are 480V motors. The transfomer I am referring to is the transfomer for the entire service to the building. Obviously there would be additional load added for lights and other power.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
What I was merely looking to ascertain is if my thinking is correct in converting the total kW of motor load into a kVA size of a transformer. This is the utility transfomer feeding the service to the building.

I have never tried to calculate the motor KW, I have simply 1HP output requires 1kVA input.

I am pretty sure someone does have idea of which motors will be running, as flow impacts piping and storage. I would not be surprised that 25% of your listed motors are off-line because they are backup units.
 

topgone

Senior Member
Lots of issues here. The VFD will nullify the power factor if it’s an AFE or not if it’s diode front end. Need the VFD pF. Also the VFDs will consume power so you need their name plates. As already mentioned if you start and accelerate real slow with a max of 100% FLA on variable torque loads only (fans, centrifugal pumps) then you can size at just 380 / 0.95 or 400 kva. In fact that may be very realistic depending on actual load. If it’s all conveyors all starting and accelerating at say 150% of FLA at the same time you’d need at least 400 x 150% or 600 kVA. You might be able to take into account some acceptable voltage drop though and trim it a little.

Also another major concern here is short circuit. Chances are highly likely that if you put more than 10 VFDs on one transformer you will need to either use lube reactors on every one or semiconductor fuses. This will seriously blow up your budget. You will probably find it’s far more economical to put say 8 VFDs per transformer and run a lot of smaller transformers.

Finally why did you pick the lowest voltage? Those motors are most likely all going to be 9 or 12 lead. So 460 is “free”. You can run smaller VFD, cheaper transformer, cheaper smaller fuses etc.
On the regenerative VFDs, it is best to ask the manufacturer if the design of their VFDs contribute to the fault currents upstream! Majority of the VFDs I know are VSIs (non-regenerative with diode front-ends) as the input diodes blocks the current that might flow back! Still, it would be wise to ask the manufacturers for clarifications!
 

topgone

Senior Member
Well honestly this is not an untypical situation where as the designer we get very little information to complete a project. The above is an example I was applying to a waste water treatment plant but I tried to keep it simple in my question. I understand the concept of what jim dungar is asking but that is information we never will receive before designing the service size for the building because honestly I do not know if there is anyway to know for sure how the motors will operate together. What they did provide was a spreadsheet list of motors with their HP and the KW rating (using 746W per HP) plus a column indicating the duty cycle either 100% or 50%. The majority of the motors we listed as 100% duty cycle. I understand we could end up with a transformer much larger than needed but since the actual usage of the motors is not known beyond the duty cycle of each motor we must design around worst case scenario. What I was merely looking to ascertain is if my thinking is correct in converting the total kW of motor load into a kVA size of a transformer. This is the utility transfomer feeding the service to the building.
Then, my best advise for you is to sum up the kVA and you're good to go!
Never use the conversion formula (HP x 0,746 = kW and divide by PF)! You should use the rated Amps x Volts/1000 = kVA instead!
 
You need to create a loading profile.

Will all of your motors be fully loaded at the same time?
Are the motors controlled by a VFD?
How many of the motors start at one time? Do some motors start while other motors are running? How long does it take for the motors to finish accelerating?
Does the NEC allow someone to decide sizing based on a loading profile? I know OP said transformer, and NEC doesn't address transformer sizing technically, but 450.3 would limit transformer undersizing.

OP said this is the utility transformer, not sure why he is sizing the POCO transformer, unless he works for the POCO.
 

LibertyEngineering

Senior Member
Location
Allentown, PA
Does the NEC allow someone to decide sizing based on a loading profile? I know OP said transformer, and NEC doesn't address transformer sizing technically, but 450.3 would limit transformer undersizing.

OP said this is the utility transformer, not sure why he is sizing the POCO transformer, unless he works for the POCO.
That is a good point NEC Article 220 for service calculations would apply. We are sizing the utility transfomer because customer is taking service from POCO at 12470V so they will own these utility transformers. There are many buildings over a large campus. This is the first building.
 
That is a good point NEC Article 220 for service calculations would apply. We are sizing the utility transfomer because customer is taking service from POCO at 12470V so they will own these utility transformers. There are many buildings over a large campus. This is the first building.
Maybe we shouldn't be calling them "utility transformers" then 😉
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Does the NEC allow someone to decide sizing based on a loading profile? I know OP said transformer, and NEC doesn't address transformer sizing technically, but 450.3 would limit transformer undersizing.

OP said this is the utility transformer, not sure why he is sizing the POCO transformer, unless he works for the POCO.
The NEC has rules for sizing service entrance conductors, feeder conductors, branch circuit conductors and their protective devices. The NEC does not provide guidance on sizing transformers themselves. Given proper terminations it is allowable to have a properly primary side protected 10kVA transformer feed a secondary 1000A switchboard.

You are correct the OP is dealing with feeder and branch circuits not service entrance circuits.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
How is it not considered the service entrance when it is the service coming into the building from the Pad Mounted Transfomer. I guess I should look up definition of Service in Article 100
The NEC defines the service entrance as the demarcation point for the power company.

If there is no power company (utility) there is no true service entrance which would follow NEC article 230.

Try not to let your industry slang get in the way when applying NEC articles, try to use the NEC definitions instead.
 

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
I agree the terms "utility and service conductors" should not be used in this context.
transformers have to be sized per a article 220 load calc.
the motors fall under 220.50
 