OK educational moment for me too..
So OP says he has 100 5HP motors @480V.
215.2(A)(1) says we have to do a art 220 load calc for the secondary feeder supplying those motors but not the transformer.
that is now understood.
So to keep it simple we use the art 430 table 430.250 for the motors rating and, our art 220 load calc is add up the motors and 25% of the largest ( one 5HP):
| | Amps | Qty | Extended | VA | Amps | kVA |
| 5hp Motor 208V 3PH | 7.6 | 100 | 760 | 631834 | 760 | 632 |
| 25% largest motor | 1.9 | 1 | 1.9 | 1580 | 1.9 | 2 |
| | | | | 633413 | 761.9 | 633 |
Then say OP's boss gets a deal on a 167 kVA padmount. There is no NEC on sizing this so boss gets to use it.
So we have a 600% OCPD on primary side and 300% on secondary right?
Primary side can be sized 6X nameplate of 167 so 7.73 Amps X 6 ~47 Amp min OCPD.
Now the secondary side is a 480V feeder OCPD and the 300% OCPD for the transformer.
What size OCPD do you all come up with for the secondary side?
I made a little graphic, pardon any end of the day mistakes.
Cheers and all happy friday.