My building department might operate like almost every other building department, but I'm not going to assume that. So let me explain the background of this thread and how my department operates.
In my building department, we send all apps thru plan review before a permit can be issued. Residential is completely separated from Commercial projects and go thru separate plan reviewers.
Residential plan review does not include any electrical at all. I have yet to see anyone even include any electrical symbols, circuits, or specs on any residential prints. Us ESI inspectors in my department never look for prints on residential projects/houses during an inspection. We go by NEC only. We have no local codes of any kind.
Commercial is totally different. All electrical specs must be included on all submissions and go thru plan review. During service, rough, and final inspections, the approved prints must be on site and the electrical installed according to the approved prints. Any deviation from the approved prints is looked at by us inspectors and considered. We then use our judgment in determining whether or not that deviation is significant enough to be considered a violation that must be corrected.
Because our Commercial plan reviewer has far more plans being submitted to review than he is capable of doing, he subs out review work to a plan review private contractor. Lately this contractor has been approving Commercial plans [which then get a much abbreviated review from our plan reviewer and then approved by our department] that don't include wire sizes. Electrical contractors have been choosing wire sizes themselves and frequently not doing it properly.
I want to run thru the process and see if anybody else has anything to add to it.
For Residential you simply go to Table310.15(B)(6)
For Commercial you can not. You [usually] must use Table310.16. But that table is alot more complicated than the residential table and it's very easy to screw-up.
You need to start by knowing which temperature column to use. 110.14(C) "Temperature Limitations. The temperature rating associated with the ampacity of a conductor shall be selected and coordinated so as not to exceed the lowest temperature rating of any connected termination, conductor, or device."
Most electrical inspectors know that the lowest rated "weakest link in the chain" is almost always the lug. Lugs for #1 and smaller wire are lab rated for 60?C, unless otherwise labeled. Lugs for #1/0 and larger wire are lab rated for 75?C, unless otherwise labeled.
So now you have the right column in Table310.16. Now to pick the right sized conductor from that column. 240.4(B) "Devices Rated 800 Amperes or Less. The next higher standard overcurrent device rating (above the ampacity of the conductors being protected), shall be permitted to be used, provided" ..... blah blah blah ..... and "(2) The ampacity of the conductors does not correspond with the standard ampere rating of a fuse or circuit breaker...". 240.6(A) lists the standard ratings for 800a or less as: 1, 3, 6, 10, 15, 20, 25, 30, 35, 40, 45, 50, 60, 70, 80, 90, 100, 110, 125, 150, 175, 200, 225, 250, 300, 350, 400, 450, 500, 600, 601, 700, 800.
For example:.....
A 90 amp limit taken from Table310.16 would require a 90 amp or smaller breaker.
A 91 amp limit taken from Table310.16 would require a 100 amp or smaller breaker.
Getting specific:
Your 100 amp service needs a 91 amp or larger rated wire from Table310.16. For #1 or smaller you're looking at the 60?C column. For this decision, it does not matter if the wire is rated 90?C. You still need to stick to the columns dictated by the lug rating. You need a #2. The #4 you get from Table310.15(B)(6) can not be used. Wrong table.
Your 150 amp service needs a 126 amp or larger rated wire from Table310.16. For #1/0 or larger you're looking at the 75?C column. You need a #1/0. The #1 you get from Table310.16 column 75?C can not be used. Wrong column for lugs connected to #1 wire. The #1 you get from Table310.15(B)(6) can not be used. Wrong table.
Your 200 amp service needs a 176 amp or larger rated wire from Table310.16. For #1/0 or larger you're looking at the 75?C column. You need a #3/0. The #2/0 you get from Table310.15(B)(6) can not be used. Wrong table.
As long as I haven't made any mistakes in my references, this is the process required to select service conductors. And every week or so I find a Commercial service wired according to Table310.15(B)(6) which has to be redone.
Any questions or comments ?
David
In my building department, we send all apps thru plan review before a permit can be issued. Residential is completely separated from Commercial projects and go thru separate plan reviewers.
Residential plan review does not include any electrical at all. I have yet to see anyone even include any electrical symbols, circuits, or specs on any residential prints. Us ESI inspectors in my department never look for prints on residential projects/houses during an inspection. We go by NEC only. We have no local codes of any kind.
Commercial is totally different. All electrical specs must be included on all submissions and go thru plan review. During service, rough, and final inspections, the approved prints must be on site and the electrical installed according to the approved prints. Any deviation from the approved prints is looked at by us inspectors and considered. We then use our judgment in determining whether or not that deviation is significant enough to be considered a violation that must be corrected.
Because our Commercial plan reviewer has far more plans being submitted to review than he is capable of doing, he subs out review work to a plan review private contractor. Lately this contractor has been approving Commercial plans [which then get a much abbreviated review from our plan reviewer and then approved by our department] that don't include wire sizes. Electrical contractors have been choosing wire sizes themselves and frequently not doing it properly.
I want to run thru the process and see if anybody else has anything to add to it.
For Residential you simply go to Table310.15(B)(6)
For Commercial you can not. You [usually] must use Table310.16. But that table is alot more complicated than the residential table and it's very easy to screw-up.
You need to start by knowing which temperature column to use. 110.14(C) "Temperature Limitations. The temperature rating associated with the ampacity of a conductor shall be selected and coordinated so as not to exceed the lowest temperature rating of any connected termination, conductor, or device."
Most electrical inspectors know that the lowest rated "weakest link in the chain" is almost always the lug. Lugs for #1 and smaller wire are lab rated for 60?C, unless otherwise labeled. Lugs for #1/0 and larger wire are lab rated for 75?C, unless otherwise labeled.
So now you have the right column in Table310.16. Now to pick the right sized conductor from that column. 240.4(B) "Devices Rated 800 Amperes or Less. The next higher standard overcurrent device rating (above the ampacity of the conductors being protected), shall be permitted to be used, provided" ..... blah blah blah ..... and "(2) The ampacity of the conductors does not correspond with the standard ampere rating of a fuse or circuit breaker...". 240.6(A) lists the standard ratings for 800a or less as: 1, 3, 6, 10, 15, 20, 25, 30, 35, 40, 45, 50, 60, 70, 80, 90, 100, 110, 125, 150, 175, 200, 225, 250, 300, 350, 400, 450, 500, 600, 601, 700, 800.
For example:.....
A 90 amp limit taken from Table310.16 would require a 90 amp or smaller breaker.
A 91 amp limit taken from Table310.16 would require a 100 amp or smaller breaker.
Getting specific:
Your 100 amp service needs a 91 amp or larger rated wire from Table310.16. For #1 or smaller you're looking at the 60?C column. For this decision, it does not matter if the wire is rated 90?C. You still need to stick to the columns dictated by the lug rating. You need a #2. The #4 you get from Table310.15(B)(6) can not be used. Wrong table.
Your 150 amp service needs a 126 amp or larger rated wire from Table310.16. For #1/0 or larger you're looking at the 75?C column. You need a #1/0. The #1 you get from Table310.16 column 75?C can not be used. Wrong column for lugs connected to #1 wire. The #1 you get from Table310.15(B)(6) can not be used. Wrong table.
Your 200 amp service needs a 176 amp or larger rated wire from Table310.16. For #1/0 or larger you're looking at the 75?C column. You need a #3/0. The #2/0 you get from Table310.15(B)(6) can not be used. Wrong table.
As long as I haven't made any mistakes in my references, this is the process required to select service conductors. And every week or so I find a Commercial service wired according to Table310.15(B)(6) which has to be redone.
Any questions or comments ?
David