kwired
Electron manager
- NE Nebraska
- EC
Load shedding is automatic method of disabling certain loads to ensure you do not go over the capacity the generator can supply, there is more then one way to do this and can be simple isolation relay that doesn't allow selected loads to run when the generator is supplying the power, or it can be more sophisticated equipment that monitors current on the generator and may allow select equipment to run if the current load level is low enough to handle the optional item. Non optional items get priority - if load is too high optional items are locked out until load goes down.But that would leave an oversized generator. Most home around here with a 200amp service get a 15 or 20kw generator with 80 or 100amp feeders going into a 200amp whole home ATS. Unless the home is all electric heat the generator runs everything during an outage, even an electric range.
Of course this might not be to code, but if it is why not do it? BTW, is there anything in code allowing this?
Art 220 load calculations often do result in a supply with higher capacity then one may normally see. People often "round up" service sizes as well. If you did a load calculation on a home and came up with needing 115 amps supply - many will install a 200 amp service though NEC would allow you to install 125. But even then you may hardly ever find that service has more then 30 or 40 amps of load, it may peak out for 15 - 30 minute periods occasionally at 70 or 80 but then drop back to the usual 30 or 40. NEC does allow you to use proper recording methods and you could possibly use that 70 or 80 amp peak for sizing a generator instead of needing one that can supply the full capacity of the 200 amp panel. That maybe puts you at a 20KVA unit , but maybe you can shed some heating appliance or something and get the load down a little further and go with the less expensive air cooled 16KVA unit instead of the liquid cooled 20 KVA unit.