300 kW generator. That sounds about right. I wonder how big the natural gas pipe run to it was
All gas as far as I know, and yes, pad mount transformer... the house is basically on a small island, but still, the load calcs are a joke.
The house isn't that big, but you did say it is on an island. Any chance they weren't considering possible future loads when sizing things?
Still could be considering more then necessary, but would justify it some.
Well it did seem pretty extreme other then if there is big future plans.You would have to see the place, believe me, the service is extremely over sized.
Well it did seem pretty extreme other then if there is big future plans.
I did a home once that was at least 10000 square feet with all electric heat. Had 4- 200 amp service disconnects mostly because it was cheaper to do that then to run a single 600 amp switch then tap to same panels I was otherwise going to use, and even with all that may still have been able to put less then a 600 amp fuse in the switch, but 400 amps would probably have been asking for at least an occasional trip.
Padmount, though surprisingly it was a 75kVA. We did have 60 kVA of electric heat plus the rest of the power for the home though.I bet the POCO hooked it up to a 50kw sow or pig without incident.
Padmount, though surprisingly it was a 75kVA. We did have 60 kVA of electric heat plus the rest of the power for the home though.
I agree, and is why I was a little surprised it wasn't a 50kVA transformer. Only time you would ever have all 60 kVA of heat running for any lengthy period is going to be in most extreme cold weather conditions, and one must also remember the transformer is in the cold ambient when that does happen, but probably is free of snow and ice accumulations75x1000/240=312amps. Pole pigs generally can take a 200% overload for an hour or two, so 600amps. So it is sized correctly in theory as long as the load isn't constant all day.
But in normal homes, even those with an electric range can get away with a 40 or 50amp service 99% of the time.
I agree, and is why I was a little surprised it wasn't a 50kVA transformer. Only time you would ever have all 60 kVA of heat running for any lengthy period is going to be in most extreme cold weather conditions, and one must also remember the transformer is in the cold ambient when that does happen, but probably is free of snow and ice accumulations
NEC in Art 702 requires generator sized to the calculated load, per Art 220. You often can do some load shedding to get the load reduced.
Ok that might explain it then. Some of these installs probably are non-complaint if the home lost power on say thanksgiving day, but it does manage to get people to agree to back up gennies.