what protects a grounded neutral that is sized smaller?
What protects the grounded neutral is the skill of the future installers and designers, just like the exception I pointed out for the ungrounded conductors.
what protects a grounded neutral that is sized smaller?
Eric, don't take this wrong but, since it is so confussing to you, why don't you send in a proposal and maybe when the CMP explains their action it might be more clear to you than the way we are trying to explain it.
You have to have current flow to generate the heat. Refer to your following example and my comment...Yes I was a bit confused at first because the earth has such a high resistance and that very little current would flow through it. But if you would examine NEC 250.66 you would note that the area(cmils) of the conductor is 1/4 of that of the ungrounded service conductor. Therefore the resistance is increased by a factor of four. This creates heat.
You are 100% correct... but you should also note that in your example, the grounded neutral conductor would be sized to carry the 100A, and keep in mind that it only sees the full 100A in the maximum imbalanced state of operation.Now let as suppose you had a 100A 3-wire single phase system. The circuit breaker is going to allow a maximum of 100A to go through. Assume that one of the ungrounded conductors is open(no load). The maximum current flowing through the neutral would be 100A. You can't just assume a partial load as being the maximum. It would be good engineering practice to assume the maximum permissible amps flowing through the circuit breaker and through the neutral as well.
Because scenarios exist where the grounded neutral does not need to carry a current equal to any one ungrounded conductor. Many loads (3? and 1? Line-to-Line) do not contribute to grounded neutral current. Therefore the maximum current the grounded neutral conductor can be expected to carry is less than that of any one ungrounded conductor. Bcause this is a variable which cannot be defined numerically for all instances, code has be written to allow the adjusted smaller size, but yet maintains that it shall never be too small. This has been true for many code cycles, and I'm sure the CMP's would have heard by now if the method implemented did in fact permit too small a grounded neutral conductor!!!So what is the purpose of 250.24(c)(1) if you know that you are going to have so many amps and that you would have to size the grounded(or neutral) conductor the same as the ungrounded conductors?
Reason and real world experience has proven otherwise.Why was this written into the code? Service conductors do have overload protection but how is the protection going to work if the code says that you are permitted to have a smaller grounded(or neutral) conductor? That cable is going to fry.
I've seen many an installation spec'd exactly this way. Perhaps there are other engineers as skeptical as youOf course in the real world we could deal with this problem very easily just by sizing the grounded conductor(or neutral) to be as large as the ungrounded conductor.
Well right now sizing the neutral is more like a guessing game. Things change. So who can be sure if they sized it properly to suit the changing load in the future? The best bet is to assume the worst case scenario. It's better than ripping out the service conductors than reinstalling them again.
I've made a career out of finding mistakes on drawings and specs
By what is told to you up front.Yes it is calculated but the calculation is based on assumptions of how many watts are connected. This can vary. How do you know that you've made the right assumptions?
Do your best to prevent an idiot from hurting himself and he'll show you that he is a better idiot than anyone could of imagined.The new owner may come in and just decide to add on more watts than was previously calculated. It's best to assume the maximum. This way you can never go wrong.
Yes it is calculated but the calculation is based on assumptions of how many watts are connected. This can vary. How do you know that you've made the right assumptions?
The new owner may come in and just decide to add on more watts than was previously calculated.
It's best to assume the maximum. This way you can never go wrong.
Forgetting the NEC and moving on to designing it is my opinion to say that we should always assume the maximum is not designing, it is just covering our rear.
To always assume the maximum may price the work out of the customers budget.
Most likely yes, but to be sure you have to do an Article 220 calculation. There is no rule that automatically permits a reduced neutral.Guys,
I have heard that the neutral can be reduced 12.5% or 70% of the size of the ungrounded conductors. I'm not sure which is right or if either one is. My question is, on a 200 amp service using 4/0 aluminum ungrounded condutors would it be acceptable to use a 2/0 aluminum neutral conductor on a 120/240 volt single phase service supplying a moblile home.