Table 310.15(B)(16) says a 14 AWG copper is good for 30 amps @ 75C and the insulation is good for 35 amps @ 90C - what is the problem? The primary function of that overload is to protect the compressor, and that inherently protects the conductor.
I am not disagreeing with some of what you have seen, but I have more often seen overloads cutting out when there is a hard starting situation then I have seen breakers trip - mostly on single phase units and usually when trying to start too soon after a stop - before refrigerant head pressure has been reduced.
Isnt 14 rated 20amps at 75*C? 25 at 90*C? Ill check my code book.
But still, if its ok to overload a conductor here, then why not allow for it in other applications?